Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MGE 7000 - 66123 NMC Communication Lost Alarm

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • MGE 7000 - 66123 NMC Communication Lost Alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-05-06 02:24 AM

0 Likes
10
2379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-06 02:24 AM

MGE 7000 - 66123 NMC Communication Lost Alarm

Hi All,

 

I have MGE 7000 UPSs using the 66123 NMC. I have configured the network settings on the NMC and I can log onto the NMV via Web Browser. However when I discover the UPS into DCE (v8.1.0), the UPS discovers and instantly gives a communication lost alarm. I cannot view the UPS Sensors or model on DCE. The Device Credentials and Community names are all correct. The MGE UPS DDF is installed on DCE.

What could be the cause for this and possible resolutions?

 

Thank you in advance.

Connecting Devices!
Labels
  • Labels:
  • Data Center Expert
  • DCIM Support
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-05-06 05:10 AM

2 Likes
1
2365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-06 05:10 AM

Hi @Tafadzwa,

 

From my experience MGE UPSs usually integrate with DCE via ModbusTCP.  I believe that the DDF for Modbus integration would be either 'MGE Galaxy EPS6/7/8k' or 'MGE Galaxy UPS'.

 

The SNMP DDF with the name that you provided is polling certain information from the device and is expecting the information from certain OIDS.  To get an SNMPwalk for comparison with the below OIDS: https://community.se.com/t5/DCE-FAQ/How-to-create-a-device-walk-file-for-Data-Center-Expert/ta-p/446...

 

Compare the below OIDs with the SNMPwalk to determine if these are valid OIDs that the device is responding to.  If the device does not have the following OIDs, then likely a Modbus integration is needed for the UPS.

  • Identifier: .1.3.6.1.4.1.705.1.1.2.0  (This OID must exist in a response from the device to use the MGE UPS DDF)

If the identifier does exist, check to see if the following OIDs get a response as well:

  • model: .1.3.6.1.2.1.1.1.0
  • serial number: .1.3.6.1.4.1.705.1.1.7.0
  • UPS Battery Status: .1.3.6.1.4.1.705.1.5.1.0
  • Battery Voltage: .1.3.6.1.4.1.705.1.5.5.0

 

If the device responds to the values and gives back a value the issue can be investigated further by technical support.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-05-08 03:47 AM

In response to Cory_McDonald
0 Likes
0
2316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-08 03:47 AM

Hi @Cory_McDonald 

 

Thank you for your reply.

 

I discovered the UPS using ModBus and it still shows the same Loss of Communication Alarm.

 

When I try to upload the MODBUS DDF, I am getting an Incorrect File Type Error, I later picked up I cannot upload any MODBUS DDFs for different Devices.

 

Is there something I need to look at that could be causing this?

 

Thank you.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-05-08 09:05 PM

0 Likes
3
2300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-08 09:05 PM

Hi @Tafadzwa,

 

When uploading Modbus DDFs ensure to use the following option within DCE: Device Menu > Modbus Device Communication Settings > Device Definition Files.  The files located on https://ddf.ecostruxureit.com should be able to be uploaded into that screen regardless of DCE version.  If you experience issues with this, I highly recommend reaching out to technical support as that is not usual behavior.

 

What Modbus DDF were you selecting from the list when discovering?  If the correct entry isn't selected the registers being polled will not align and the device will go immediately into lost communication after attempting the Modbus Discovery.

 

How did the results of the SNMPwalk go and checking it against the information I previously provided?

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-05-15 04:04 AM

In response to Cory_McDonald
0 Likes
2
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-15 04:04 AM

Hi @Cory_McDonald 

 

Thank you for your feedback and assistance. I am working on a remote Project with a Partner. We had a call and I managed to upload the DDF File however the Modbus DDF File is already pre-installed on DCE. 

We Discovered the MGE Galaxy 7000 UPS using the DDF MGE Galaxy EPS6/7/8k but the issue of "Communication Lost" still persists.

I did not get the chance to compare the OIDs you provided me with the SNMPwalk File however I have asked the partner on Site to do so and revert with feedback.

 

I'm aware the NMC 66123 has no replacement however is there any other NMC that can be used on the Galaxy 7000?

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-21 12:31 PM

In response to Tafadzwa
0 Likes
1
2093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-21 12:31 PM

Hi @Tafadzwa,

 

I am unsure about what NMCs would be supported inside of that unit, but you should be able to contact your local technical support / sales to check into that for you.

Were you able to work with your customer to solve the communication lost with the unit?

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-08-22 07:24 AM

In response to Cory_McDonald
0 Likes
0
2077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-22 07:24 AM

Hi @Cory_McDonald ,

 

We opted to go for a different network card, still waiting to receive the shipment.

 

Will advise after installation if the recommended replacement works perfectly.

 

Regards,

 

Tafadzwa.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

wasabi
wasabi Contributor
Contributor

Posted: ‎2026-01-21 10:51 PM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-21 10:51 PM

Hi all,

sorry to bump this old thread up but just checking if MGE NMC 66123 is compatible DCE v8 and above ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Dominique38 Explorer
Explorer

Posted: ‎2026-01-21 11:43 PM . Last Modified: ‎2026-01-21 11:43 PM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-21 11:43 PM . Last Modified: ‎2026-01-21 11:43 PM

Hi,

No, MGE NMC 66123 is not compatible anymore with DCE from 7.9.0 version !

=> you can replace the card with an AP9635 + mecanical part + electronic adaptation card

Reply

Link copied. Please paste this link to share this article on your social media post.

wasabi
wasabi Contributor
Contributor

Posted: ‎2026-01-22 09:03 PM

0 Likes
0
916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-22 09:03 PM

thanks, last question. how about the card 66061 MGE JBus/Modbus Card ? if so would you have any emails about this ? many thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Dominique38 Explorer
Explorer

Posted: ‎2026-01-22 11:30 PM

0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-22 11:30 PM

MGE 66061 Modbus card is still available

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore