Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Invalid Network Address or time out on DCE Client

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Invalid Network Address or time out on DCE Client
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
AhmedAzzam2200
AhmedAzzam2200 Explorer
Explorer

Posted: ‎2022-03-29 02:43 PM

0 Likes
5
3990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-29 02:43 PM

Invalid Network Address or time out on DCE Client


Hi Everyone,

 

I have an issue in DCE Client V7.8.1 when I try to Log in DCE server by DCE Client, I get the error ( Invalid Network Address or time out) in DCE Client. while I Can access the server by the web as shown in the attached Pics.

I tried to increase the time out, change the port number, using HTTP and HTTPS ports and they didn't work yet.

 

Thanks in advance,

Attachments
Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Jef Leader
Leader

Posted: ‎2022-04-05 01:30 AM . Last Modified: ‎2022-04-05 01:31 AM

In response to AhmedAzzam2200
1 Like
2
3879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-05 01:30 AM . Last Modified: ‎2022-04-05 01:31 AM

Hi Ahmed,

 

Try checking the client logs to see if there should be any useful info. Client log file usually located in Win. C:\Users\<username>\.isxc\7.8.1\.metadata\.log

 

If the client is unable to connect to server, then it might be network/routing related. Maybe something like firewall, antivirus program, proxy server, VPN, etc. 'located' between the client and server not permitting the desktop client to connect (but permitting the http/https connections).

 

Kind regards,

Jef

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Jef
Jef Leader
Leader

Posted: ‎2022-03-30 01:22 AM

0 Likes
4
3952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 01:22 AM

Hi Ahmed,

 

It seems you are trying to connect (login) to servers private LAN, that is not supported for desktop client access.

Assuming the server is configured/setup properly, it should usually have 2 network interfaces: Public (LAN1) and Private (LAN2). 
You can try to login via the IP address for the Public/LAN2 that you have assigned (configured during the installation).

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AhmedAzzam2200
AhmedAzzam2200 Explorer
Explorer

Posted: ‎2022-04-04 03:50 AM

In response to Jef
0 Likes
3
3897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-04 03:50 AM

Dear Jef,

 

I tried to connect to the server through Private and public Networks and it doesn't work for both.


Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2022-04-05 01:30 AM . Last Modified: ‎2022-04-05 01:31 AM

In response to AhmedAzzam2200
1 Like
2
3880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-05 01:30 AM . Last Modified: ‎2022-04-05 01:31 AM

Hi Ahmed,

 

Try checking the client logs to see if there should be any useful info. Client log file usually located in Win. C:\Users\<username>\.isxc\7.8.1\.metadata\.log

 

If the client is unable to connect to server, then it might be network/routing related. Maybe something like firewall, antivirus program, proxy server, VPN, etc. 'located' between the client and server not permitting the desktop client to connect (but permitting the http/https connections).

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AhmedAzzam2200
AhmedAzzam2200 Explorer
Explorer

Posted: ‎2022-04-07 01:47 AM

In response to Jef
0 Likes
1
3836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-07 01:47 AM

Dear Jef,

thank You for Your replay actually, I checked it and  it was a problem with Antivirus Firewall as you said, Thanks a lot

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2022-04-07 01:54 AM

In response to AhmedAzzam2200
1 Like
0
3834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-07 01:54 AM

Hi Ahmed,

 

You are welcome & many thanks for the update.

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore