New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
EMCP 4 generator integration
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-2602:39 PM
EMCP 4 generator integration
Hello! Could you help me, I integrated an EMCP 4 generator to the DCE but when the equipment is alarmed the notifications do not arrive and the DCE does not appear alarmed.
2)If there are predefined alarms, what is the polling interval for the device? you can check this in Device -->snmp/modbus device comm settings --> device scan settings. Edit the device and lower the polling interval to 1 or 2 mins. This way when an alarm occurs, DCE will see it in a min or 2
3) if the above is true and you still missed an alarm, it's possible it wasn't active for longer than 1 min. This is unlikely with a generator, but possible.