Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Difference in Device Count

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Difference in Device Count
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
ϟϟ
ϟϟ Explorer
Explorer

Posted: ‎2021-08-13 09:57 AM

0 Likes
5
3306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 09:57 AM

Difference in Device Count

Hi,

 

I'm just wondering why the device count varies in Data Center Expert?
Referring to the image below, these are the reported counts:

137 Devices - Shown in the status bar, and if we click 'All Devices' in the Device Groups Pane
140 Devices - If we sum up manually, all the devices in each of the individual folder,  in the Device Groups Pane
147 Devices - If we sum up all the device count in device type inventory report

Hope someone can help me clarify this issue.

 

Thanks.

Device count difference in Monitoring TabDevice count difference in Monitoring TabDevice count difference in ReportingDevice count difference in Reporting

Attachments
Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • dce
  • device count
  • devices
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-08-13 01:36 PM

In response to ϟϟ
0 Likes
2
3292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 01:36 PM

Hi @ϟϟ ,

 

I'm unable to replicate that here in NAM. I have 90 devices in "All Devices" and each main sub group count adds up. I verified and counted every device in every level 1 folder.

 

I also went to your server and manually counted each group's devices. They did add up to 140. Unsure why the count when looking at All Devices is reading 137. Is it possible that the same device is in multiple groups? That is possible to do, you can hold the control key and drag and drop. I don't usually mention it as I have seen strange behavior. Have you checked with Shaun or any of the guys that might administer that server to see if they've seen any weird issues?

 

Is this also a customer issue or is it just something on the EMEA server?

 

Steve

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-08-13 10:31 AM . Last Modified: ‎2021-08-13 10:32 AM

0 Likes
4
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 10:31 AM . Last Modified: ‎2021-08-13 10:32 AM

Hi @ϟϟ 

 

If you look closely at the Device Type Inventory Report, you will see that the 2nd row down is listed as camera pods. A bit closer to the bottom, you have a row for sensor pods. There are 5 of each. That would seem to account for the 10 count difference. I believe the count on the count on device view with everything highlighted notes all devices that take up a node license or a virtual device. It does not account for a pod that is part of a NetBotz appliance.

 

Sorry, I'm not sure how you got the 140.

 

Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ϟϟ
ϟϟ Explorer
Explorer

Posted: ‎2021-08-13 12:42 PM

In response to APC_Steve
0 Likes
3
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 12:42 PM

Hi @APC_Steve,

 

I appreciate your prompt reply!

Hope the image gives better idea how I got it to 140 devices.

There are 9 folders, under All Devices.

Basically, I just click on each of the folder, and adds all the values shown in the red circle. 

 

Sum of devices in each folderSum of devices in each folder

 

Thank you!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-08-13 01:36 PM

In response to ϟϟ
0 Likes
2
3293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 01:36 PM

Hi @ϟϟ ,

 

I'm unable to replicate that here in NAM. I have 90 devices in "All Devices" and each main sub group count adds up. I verified and counted every device in every level 1 folder.

 

I also went to your server and manually counted each group's devices. They did add up to 140. Unsure why the count when looking at All Devices is reading 137. Is it possible that the same device is in multiple groups? That is possible to do, you can hold the control key and drag and drop. I don't usually mention it as I have seen strange behavior. Have you checked with Shaun or any of the guys that might administer that server to see if they've seen any weird issues?

 

Is this also a customer issue or is it just something on the EMEA server?

 

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ϟϟ
ϟϟ Explorer
Explorer

Posted: ‎2021-08-13 02:32 PM

In response to APC_Steve
0 Likes
1
3288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-13 02:32 PM

Hi @APC_Steve,

 

Thank you for going the extra mile 🙂

 

Since this is a test server and I didn't really checked, the possibility of same device exist in multiple groups is actually a good reason why this happens.

 

Worry not, this is not a customer issue or anything, it's just me trying to crosscheck the API for device count, in DCE.
FYI, the API returns 147, which is tally with the report. 

 

Thank you again.

 

Have a great weekend!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2021-08-16 01:59 AM . Last Modified: ‎2021-08-16 02:00 AM

In response to ϟϟ
0 Likes
0
3274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-16 01:59 AM . Last Modified: ‎2021-08-16 02:00 AM

Hi @ϟϟ 

 

If this is the server on the Galway lab, we do indeed have devices that are members of multiple folders.  For example, the two devices with IP addresses in the folder named EU-something, also appear in the folder EMEA.

 

I haven't gone through every folder looking for these, so I can't give you a solid number - but hopefully a concrete example will show you what you're looking for, or at least why the discrepancy exists.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore