New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Data Center Expert monitoring of MGE UPS with NMC 66074
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-1512:37 AM
Data Center Expert monitoring of MGE UPS with NMC 66074
Hi All, I have MGE UPSs that have an NMC 66074 that I want to monitor via DCE v8.1.0 however when I discover the UPSs into DCE, I am getting a Failure Alarm saying "Communication with 'UPS IP' has been lost.
I have added the UPS Credentials on DCE and I can Log onto the UPS via a Web Browser with no issues.
What could be causing this and how can it be resolved?
I am assuming that this device is being discovered into DCE via ModbusTCP. When discovering a ModbusTCP device into DCE it is always "discovered", but if DCE is unable to communicate to it, you will receive the "Communication has been lost" alarm.
Ensure that ModbusTCP communication is enabled on the card, network ports are open for the communication on the desired port, and the correct DDF for that device type are being selected during discovery.
If you are having issues beyond those, please reach out to technical support for additional guidance.