DCE - Schneider Galaxy VS 50kW UPS - Network Management Card 4 - Can't configure in DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE - Schneider Galaxy VS 50kW UPS - Network Management Card 4 - Can't configure in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
brucep26b
Crewman brucep26b
Crewman

Posted: ‎2020-06-03 04:28 PM

0 Likes
3
2257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 04:28 PM

DCE - Schneider Galaxy VS 50kW UPS - Network Management Card 4 - Can't configure in DCE

HI there

 

I have the above a UPS i want to monitor in DCE.

 

IT is Schneider Galaxy VS 50kW UPS with a Network Management Card 4

 

I cannot get it added to  DCE . I an only trying via basic SNMPv1 at the moment and tried everything. I will set it up using SNMP3 if i can get DCE to see device eventually.

 

I cannot connect o it via DCE.

 

I cannot SNMPWALK to it via DCE.

 

I CAN SNMPWALK to it from my command line on PC using devicewalk no problem at all.

 

I thought because they are both Schneider products it should be pretty easy.

 

I don't believe there would be any firewall rules in place preventing this as I am adding devices to DCE all the time.

 

any thoughts?

 

cheers

 

Bruce

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
brucep26b
Crewman brucep26b
Crewman

Posted: ‎2020-06-09 04:13 PM

In response to brucep26b
0 Likes
0
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-09 04:13 PM

UPDATE

 

A firewall rule needed to be updated

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Shaun
Commander Shaun Commander
Commander

Posted: ‎2020-06-04 04:27 AM . Last Modified: ‎2020-06-04 04:32 AM

0 Likes
2
2245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-04 04:27 AM . Last Modified: ‎2020-06-04 04:32 AM

Hi Bruce,

 

Could I clarify, are you using the snmpwalk function on the status page of the DCE?  Also could we double-check that on the NMC, there's no NMS IP set in the SNMP settings (Configuration->Network->SNMPv1->Access Control - it'd be useful to set these to 0.0.0.0 while testing, and narrow them if needed once we're up and running).

 

Can I also ask if these devices are on the same or separate networks?  If Ping Response is enabled on the NMC4 (Configuration->Security), can we try ping from the same DCE status page?

 

There's a very high probability that this is a connectivity issue, as the snmpwalk functionality does not depend on anything particularly unique about the DCE nor the NMC4, so we need to narrow down what would cause the NMC4 to answer one but not the other.

 

I can confirm you should expect this combination to work - we have a GVSUPS50KH with DCE 7.8.0 in our local lab, so I've tested this first-hand.  There are some minor teething issues as the NMC4 is a very new platform, but SNMP should not be one of them.

Reply

Link copied. Please paste this link to share this article on your social media post.

brucep26b
Crewman brucep26b
Crewman

Posted: ‎2020-06-04 02:16 PM

In response to Shaun
0 Likes
1
2228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-04 02:16 PM

Hi Shaun

 

Could I clarify, are you using the snmpwalk function on the status page of the DCE? 

Yes that is correct.

Also could we double-check that on the NMC, there's no NMS IP set in the SNMP settings (Configuration->Network->SNMPv1->Access Control - it'd be useful to set these to 0.0.0.0 while testing, and narrow them if needed once we're up and running).

Yes that is correct. I have tried with 0.0.0.0 and narrowed it down as well. Still no go.

 

Can I also ask if these devices are on the same or separate networks? 

They are on a separate network. however just about if not all our devices are on different network to DCE server.

 

If Ping Response is enabled on the NMC4 (Configuration->Security), can we try ping from the same DCE status page?

Yes it is enabled. I can ping fine from PC. I Can't ping from the DCE Status page. Good call. didn't try this option.

 

There's a very high probability that this is a connectivity issue, as the snmpwalk functionality does not depend on anything particularly unique about the DCE nor the NMC4, so we need to narrow down what would cause the NMC4 to answer one but not the other.

I agree. I have a Ticket in with our Network team as well. Thought i put it on the forum there in case something is know with NMC4

 

I can confirm you should expect this combination to work - we have a GVSUPS50KH with DCE 7.8.0 in our local lab, so I've tested this first-hand.  There are some minor teething issues as the NMC4 is a very new platform, but SNMP should not be one of them.

Yes it should be pretty easy to setup this device. There is nothing special about the site this was put in at.

 

Thanks for your help

 

cheers

Bruce

 

Reply

Link copied. Please paste this link to share this article on your social media post.

brucep26b
Crewman brucep26b
Crewman

Posted: ‎2020-06-09 04:13 PM

In response to brucep26b
0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-09 04:13 PM

UPDATE

 

A firewall rule needed to be updated

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore