Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE SNMPv3

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE SNMPv3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Nirmolak
Nirmolak
Explorer

Posted: ‎2024-05-31 08:19 PM

0 Likes
3
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-31 08:19 PM

DCE SNMPv3

I have Raritan IPDUs registered in DCE via SNMP v1.

 

I wish to upgrade them to SNMP v3, and re-register them via SNMP v3 into DCE. 

 

Based on testing, the only way is to remove the device, then re discover them via SNMP v3. 

 

But this causes me to lose all historical data as well virtual sensors. 

 

Is there any way to change from SNMP v1 to v3 for Raritan devices without losing history? 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-06-03 08:54 AM

1 Like
0
1610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-03 08:54 AM

Hi @Nirmolak,

 

Currently there is no way to switch 3rd party devices from SNMPv1 to SNMPv3 without deleting and rediscovering the device.

 

Our engineering team is currently working on an easy way to switch devices between SNMPv1 and SNMPv3 and it is currently expected to launch in the next version of Data Center Expert.  To stay up to date on release notifications you can log into the EcoStruxure IT Entitlements site and follow the directions here: https://ecostruxure-it-entitlements.se.com/csm?id=kb_article_view_cs&sysparm_article=KB0018943

 

If you do not have access to EcoStruxure IT Entitlements for your account, please reach out to technical support.

 

Kind Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Gabi
Gabi
Mentor

Posted: ‎2024-06-03 04:08 AM

1 Like
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-03 04:08 AM

Hello,

 

from what I know you cannot switch to snmp v3 without removing and rediscover....since every device receive an id number(in DCE database and config) even if you remove and rediscover any device without any config change(ip,hostname,snmp), the new discovered device receive a new id without any pointers to the old id

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-06-03 08:54 AM

1 Like
0
1610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-03 08:54 AM

Hi @Nirmolak,

 

Currently there is no way to switch 3rd party devices from SNMPv1 to SNMPv3 without deleting and rediscovering the device.

 

Our engineering team is currently working on an easy way to switch devices between SNMPv1 and SNMPv3 and it is currently expected to launch in the next version of Data Center Expert.  To stay up to date on release notifications you can log into the EcoStruxure IT Entitlements site and follow the directions here: https://ecostruxure-it-entitlements.se.com/csm?id=kb_article_view_cs&sysparm_article=KB0018943

 

If you do not have access to EcoStruxure IT Entitlements for your account, please reach out to technical support.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

JLehr
JLehr Champion
Champion

Posted: ‎2024-06-04 12:51 PM . Last Modified: ‎2024-06-04 12:51 PM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 12:51 PM . Last Modified: ‎2024-06-04 12:51 PM

There are several ways to be notified about software releases. You can opt in to notifications in the Entitlements portal, and you can subscribe to what interests you in the forum and help center.

See how

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore