New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
DCE/DCO virtual servers migration: Best Practices
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-10-2803:55 PM
DCE/DCO virtual servers migration: Best Practices
Hi Everybody: A Colocation company is requiring from us migrate existing DCE/DCO virtual servers into a new ones (Including next modules: Capacity, Change, Insight , Energy efficiency & cluster)
As I understand licenses are tied to the MAC address.
Beside that, do you have additional recommendations or a kind of best practices to grant success?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-10-2902:16 AM
Hi Victor,
I can only speak for the DCE but here is the general outline.
Firstly, the physical DCE will need a software support contract including all the nodes that need to be migrated,
Next the customer will need to deploy a DCE VM on the same DCE version as the hardware appliance, the spec of the VM should follow the VM spec guide. If the DCE is not running the latest version (7.8), you can upgrade before or after the migration but the physical appliance and the VM must be on the same version after this step.
Take a backup of the physical appliance using the in-built backup utility.
Restore that backup to the new DCE VM.
Contact support with the old MAC/serial/pass-codes and the new MAC/serial so that the licences can be migrated.
Configure a schedule backup job with the in-built backup tool on the new VM.
(This is not required but I can not recommend it enough)