Raised Floor and Dropped Ceiling Leakage Update
The Room menu now shows airflow leakage details for the raised floor and dropped ceiling.
We havenβt changed any calculations, but here is some additional background information. The airflow leakage velocity π at any location is related to the pressure drop Ξπ across the raised floor or dropped ceiling by:
Ξπ=π(1/2)ππ2
where π is the density of air (we assume 1.2 kg/m3 at seal level) and π is the dimensionless loss coefficient. We compute π as a function of open area π½ for all resistances in EcoStruxure IT Advisor CFD from [1]:
π=(1/π½2.3)(1βπ½)
Note that π½ in the above equation is a decimal value, not a percentage. For example, 0.01 instead of 1%. Finally, % open area values selected for the various raised floor and dropped ceiling leakage options are based on [2] and [3].
1. VanGilder, J., Seymour, M., Hu, B., Tian, W., Pang, M., and Lin, C., 2022 βFlow Resistance Characteristics for Data Center CFDβ, ASHRAE Transactions 2022, Volume 128, Part 2. 2. VanGilder, J., and Zhang, X., 2015, βDevelopment of a Raised-Floor Plenum Design Toolβ, Proceedings of InterPACK, July 6-9, San Francisco, California. 3. VanGilder, J. And Zhang, X. 2014, βCooling Performance of Ceiling-Plenum-Ducted Containment Systems in Data Centersβ, Proceedings of the Intersociety Conference on Thermomechanical Phenomena in Electronic Systems (ITHERM 2014), May 27β30, Orlando, Florida.