Connect with IT Design CFD software users to optimize data center equipment layout, cooling, and energy consumption using computational fluid dynamics (CFD).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New InviteClose
Invite a Colleague
Found this content useful? Share it with a Colleague!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-1907:01 AM. Last Modified: 2021-10-1907:15 AM
Limited Cooler Capacity
Hi everyone, we have a major update for the coolers in ITA CFD.
Users can now specify a limited cooling capacity for each cooler.
The capacity can now be set as ‘infinite’ (the default – and equivalent to the previous modeling approach) or ‘specified’.
In the ‘specified’ model, the cooler’s actual supply temperature may not be equal the specified ‘setpoint’ temperature. If the load exceeds the cooler capacity under the current operating conditions, the supply temperature will also exceed the setpoint temperature.
The ‘specified’ capacity model takes two data points as input and assumes a linear relationship between return temperature and capacity. This data is entered for a known reference airflow rate which usually corresponds to the cooler’s maximum airflow as this is the data most often published by cooler manufacturers.
After simulation is complete, you can hover the mouse over the cooler to see the supply temperature, average return temperature, load, and capacity.