Passing DI signal to DO signal within EAE

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • Passing DI signal to DO signal within EAE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Start a Topic
Solved
Eyanto
Ensign Eyanto
Ensign

Posted: ‎2025-08-20 09:23 PM

0 Likes
5
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-20 09:23 PM

Passing DI signal to DO signal within EAE

Hi All, 

Still new in EAE and hope to get some helps from the community.

We have configured the application to symlink Modicon STB into EAE which consists of DI and DO signals.

We managed to get the DI signal from Modicon STB using DisplayBool FB and also managed to trigger the DO signal to Modicon STB using SetBool FB as shown by below pictures.

DisplayBool FB.jpeg

 

SetBool FB.jpeg

Now, we are required configure inter-link logic between the DI and DO. However, there is only single connection point from both FBs. Kindly guide us. Thanks

 

 

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Eyanto
Ensign Eyanto
Ensign

Posted: ‎2025-09-02 09:13 PM

In response to theo.bagieu
0 Likes
0
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-02 09:13 PM

Hi @theo.bagieu, thank you for following up.

 

Yes, we managed to solve the issue with help from SE Malaysia support as well. 

Utilizing Island_Word2Bit FB, split the output to DisplayBool and N1 FBs. N1 FB acts as OR gate receiving the signal from sensor 1 or 2 to trigger the output. In the same time, it can also receive manual input from SetBool FB for Lamp Test function. Below are the logic snapshots.

 

Island-Word2Bit Split Outputs.png

N1 FB for Interlink.png

Thank you again for your recommendations. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
theo.bagieu
Ensign theo.bagieu Ensign
Ensign

Posted: ‎2025-08-25 12:38 AM . Last Modified: ‎2025-08-25 12:39 AM

0 Likes
1
598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-25 12:38 AM . Last Modified: ‎2025-08-25 12:39 AM

Hi @Eyanto 
I will assume that your request is not only to link DI to the DO but you want to keep your HMI SetBool and DisplayBool Logic.

I will consider 3 major solutions there, depending on your needs :

  • Create your own CAT, with custom logic to Display/Set your bool(s) either from the application or the HMI, but you will have to manage yourself bypassing, forcing control etc etc.
  • Kept the SetBool & DisplayBool and use a DS_SELECTX block. This FB helps you to select between two data depending on which event input is triggered. In your use case, your HMI could be on REQ1/DI1_1 and your loopback from the IO on the REQ2/DI2_1.
     theobagieu_0-1756106445372.png
  • If you wish to had a advanced & complete I/O control, you can use the FB from the AppCommonProcess or App2CommonProcess like DigitalInput & DigitalOutputtheobagieu_1-1756107461708.png

    These will have a complete HMI support, alarm management, and process library integration.

    Hope it helps

Reply

Link copied. Please paste this link to share this article on your social media post.

Eyanto
Ensign Eyanto
Ensign

Posted: ‎2025-08-26 06:02 PM

0 Likes
2
570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-26 06:02 PM

Hi @theo.bagieu , 

Your assumption is correct. We would like to retain the SetBool and Display Bool FBs while creating another interlink DI and DO.

 

Besides that, thank you for you suggestions. We will try them out. 

Reply

Link copied. Please paste this link to share this article on your social media post.

theo.bagieu
Ensign theo.bagieu Ensign
Ensign

Posted: ‎2025-09-02 01:53 AM

In response to Eyanto
0 Likes
1
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-02 01:53 AM

@Eyanto is your issue solved ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Eyanto
Ensign Eyanto
Ensign

Posted: ‎2025-09-02 09:13 PM

In response to theo.bagieu
0 Likes
0
523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-02 09:13 PM

Hi @theo.bagieu, thank you for following up.

 

Yes, we managed to solve the issue with help from SE Malaysia support as well. 

Utilizing Island_Word2Bit FB, split the output to DisplayBool and N1 FBs. N1 FB acts as OR gate receiving the signal from sensor 1 or 2 to trigger the output. In the same time, it can also receive manual input from SetBool FB for Lamp Test function. Below are the logic snapshots.

 

Island-Word2Bit Split Outputs.png

N1 FB for Interlink.png

Thank you again for your recommendations. 

Reply

Link copied. Please paste this link to share this article on your social media post.

nawawiid
nawawiid
Cadet

Posted: ‎2025-09-17 02:04 AM

In response to theo.bagieu
0 Likes
0
423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 02:04 AM

Hi @theo.bagieu 

Regarding on your solution for Yanto

nawawiid_0-1758099382649.png

I already try this method, but DO output value not trigger (passing)

nawawiid_1-1758099791811.png

thanks in advance Mr.Theo

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore