Modbu TCP communication between EAE app and a third party PLC

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • Modbu TCP communication between EAE app and a third party PLC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Start a Topic
ibrahim.rebouh
Ensign ibrahim.rebouh
Ensign

Posted: ‎2025-11-23 11:56 PM

0 Likes
2
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-23 11:56 PM

Modbu TCP communication between EAE app and a third party PLC

Hello everyone,

I’m working on a project where a Siemens S7-1200 PLC writes data via Modbus TCP to the holding registers of my PLC.
I would like to use EcoStruxure Automation Expert (EAE) for this application and install an M251 dPAC so the S7-1200 can write data to it.

Could anyone provide documentation or guidance on how to set this up on the EAE side (which function blocks to use, configuration steps, examples, etc.)?

Thank you in advance!

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
theo.bagieu
Ensign theo.bagieu Ensign
Ensign

Posted: ‎2025-11-25 12:35 AM . Last Modified: ‎2025-11-25 12:37 AM

1 Like
1
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-25 12:35 AM . Last Modified: ‎2025-11-25 12:37 AM

Hi @ibrahim.rebouh,

I assume in your use case that the M251d will be the modbus TCP Server (slave).
You need to use the library 'Standard.IoModbusSalve' 

Thanks to that library you will be able to setup a ModbusTCP server in your device HardwareConfiguration.
This is the default structure to define : 

theobagieu_0-1764059258734.png


Then, under MODBUSGENBC, you can add the registers or coils you would like to expose into the server.

The last step is to configure the properties : In MODBUS node properties, set up the IP address to the same ip than your M251d. You can edit some other properties like port etc...
Also, if required, in MODBUSGENBC, you can change the station id along with some other parameters.

Finally, for each added registers in the configuration, you can change the register type (Holding Register/Input Register, the addresses of the registers etc...)
You can find more information about this step in UserManual (UserManual > Ecostruxure Automation Expert - Buildtime Network Communications > Modbus > Manual Development)

 

Edit: Then you can create symlink in your application, and map them to the exposed registers in you hardware configuration.

Hope this helps

Reply

Link copied. Please paste this link to share this article on your social media post.

ibrahim.rebouh
Ensign ibrahim.rebouh
Ensign

Posted: ‎2025-11-25 03:45 AM

In response to theo.bagieu
0 Likes
0
131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-25 03:45 AM

Hi @theo.bagieu,

Thank you for the reply you have been a great help, i'll test it out and see.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore