Connect to device (M251d)
Hello,
I would like to connect to my M251d, following the instructions on the documentation with the login installer / *********, but the PLC is always rejecting the connection.
Check the picture below:
Is there a way to do a factory reset ?
Thank you.
- Labels:
-
EcoStruxure Automation Expert
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-10 03:59 AM
Hi
from the snap the M251d is already configured using another solution and hence the default credentials is no more valid.
if you donot remember the credentials, only way is to reset the device. Please refer to the M251d user manual installed with SW.
Refer to the below chapter on how to use SD Card to reset device.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-10 03:59 AM
Hi
from the snap the M251d is already configured using another solution and hence the default credentials is no more valid.
if you donot remember the credentials, only way is to reset the device. Please refer to the M251d user manual installed with SW.
Refer to the below chapter on how to use SD Card to reset device.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.