ETL integration examples

ETL examples, troubleshooting, and tips

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ETL - Extract Transform Load
  • ETL examples, troubleshooting, and tips
  • ETL integration examples
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • ETL integration examples
  • Manually upload JDBC drivers
  • ETL Postgres database connection
  • ETL integration examples
  • Manually upload JDBC drivers
  • ETL Postgres database connection

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ETL examples, troubleshooting, and tips
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4527 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ETL integration examples

Sisko JLehr Sisko
‎2023-12-21 09:36 AM

These example templates can be uploaded to the server to import example data, typically from an Excel sheet. They provide a good starting point for developing your own transformations.

 

Network Ports and Network Connections Import Example

 

The files below show how port configurations and network connections can be imported with ETL.

To use the template:

 

  1. Upload the files below to the /data/pentaho/import folder.
  2. Create a new staging database.
  3. Setup a new ETL Integration in the ITA client, and choose the "Network Import" job/transformation.
  4. After the initial synchronisation has been done, associate the new devices to equipment.
  5. Force the synchronisation to run again, or wait for the next scheduled synchronisation to run. The network ports and connections should be imported and added to the associated equipment.

The ETL integration examples.zip file attached below contains:

  • Network Import.kjb 
  • PortConfiguration.ktr 
  • Network.ktr 
  • ConfigurationItems.ktr 
  • Connections.xls 

 

Import Examples

 

This section focuses on how to model real-life "scenarios" in the import database, and where the information is used/displayed inside EcoStruxure IT Advisor. 

 

Entity

 

To add a simple entity with only a few properties, only the CONFIGURATION_ITEM table is needed (Figure 1). The references to CONFIGURATION_ITEM_TYPE is used to identify the type of the items.

 

Figure 1

ETL_Staging_specification_pdf__page_22_of_36__1.png

 

Simple Measurements

 

In slightly more complicated cases where simple measurements are associated with the ConfigurationItems, the following general data structure is needed. See Figure 2. This associates an average powerdraw of 193.5W to Odin (server_01). 

 

Figure 2

 

ETL_Staging_specification_pdf__page_22_of_36__2.png

Advanced Power Measurements

 

More advanced power measurements can be modeled by using the cim_subid field. See Figure 3. The field cim_subid is used to group measurements – in this case phase power measurements from a breaker-module in a pdu.


The id used in cim_subid is used inside IT Advisor to enable branch circuit monitoring by matching the id to breaker names set up in IT Advisor.

Please note that you have to provide both an average and a peak power measurement (the example in Figure 3 is for the peak measurement). Also note that that you have to specify the start and end time for the measurement. The time is given in ms since January 1st 1970.

 

Figure 3

 

ETL_Staging_specification_pdf__page_23_of_36_.png

Temperature Sensors

 

To make it possible to use temperature measurements from external systems in the Cooling Simulations, they need to be modeled as shown in Figure 4. It is not necessary to provide all three different types of temperatures.
Each temperature measurement will result in one sensor inside IT Advisor, with the assigned temperature reading. The name of the sensor will be set to "temperatureSensor "+cim_subid. 

 

Figure 4

 

ETL_Staging_specification_pdf__page_24_of_36_.png

Alarm

 

Alarms are associated with Configuration Items, therefore both the CONFIGURATION_ITEM and ALARM table are needed. Because of the database-constraints on these tables, the Configuration Item needs to be updated before the Alarm. Alarms will show up in IT Advisor even if the external device is not associated with a DataCenterItem in the IT Advisor model. 

 

Figure 5

 

ETL_Staging_specification_pdf__page_24_of_36_.png

Tag

 

The data structure needed to map tags is shown in the diagram in Figure 6. 
This associates the tag "sales" to the server Odin (server_01). Once the external device (Odin) has been associated with an item in the IT Advisor model, the tag will be associated with that item. If the tag does not already exist, it is created with the cip_value as a description.

 

If the tag is marked deleted (state_flag set to "deleted"), the tag will be unassociated from the associated DataCenterItem. The tag itself will NOT be deleted from the IT Advisor model.


If the external item (Odin) is unassociated, the DataCenterItem will retain all tags, including those created through ETL. Subsequent changes in ETL to the tag are NOT reflected to the IT Advisor model. 

 

Figure 6

ETL_Staging_specification_pdf__page_25_of_36_.png

 

 

Custom Property

Custom properties are mapped in the same way as tags, only the classification (property type) differ. In this example (Figure 7) the property "owner=sales" is associated with Odin. Once the external item Odin is associated with a DataCenterItem, the CustomProperty "owner" will be created with the value "sales", and assigned to the DataCenterItem. If the property is marked deleted, it will be removed from the IT Advisor model.

If external item is unassociated, the DataCenterItem will retain all its CustomProperties including those created through ETL. 

 

Figure 7

 

ETL_Staging_specification_pdf__page_26_of_36_.png

Network Connection

 

Modeling of network connections is done by using CONFIGURATION_ITEM_RELATION and its related tables – most importantly the RELATION_ENDPOINT_PROPERTY table that is used to model information about network-ports.


The requested data-structure can be seen in the diagram (Figure 8). The properties related to the network port, is used inside IT Advisor to create PortConfiguration objects.


Among other things the PortConfigurations maintain a range of ports. The ETL synchronization job will try to make the smallest number of PortConfigurations for a piece of network equipment, by using port-ranges. To aid in this, the module-name is used for grouping. 


Whenever module_name and connector_type match, the range of existing ports will be extended to include new ports (otherwise outside of range) -> you can't have the same module split in two different ranges eg. 1-15 and 16-32


Network connections and port configurations are only added to the IT Advisor model if both ends of the relation are associated with data center items. 

 

The communication speed that a network-port can handle should be provided with one of the units "Kbps", "Mbps", "Gbps" or "Tbps". 

 

The port type must be one of the following: FIBER_REGULAR, FIBER_UPLINK, RJ45_REGULAR, RJ45_UPLINK, APC_LAN_REGULAR, APC_LAN_UPLINK, IP_KVM_UPLINK, IP_KVM_REGULAR, FIBER_SC_REGULAR, FIBER_SC_UPLINK, FIBER_LC_REGULAR, FIBER_LC_UPLINK, FIBER_ST_REGULAR, FIBER_ST_UPLINK, FIBER_MTRJ_REGULAR, FIBER_MTRJ_UPLINK, FIBER_FC_REGULAR, FIBER_FC_UPLINK, FIBER_MPO_MTP_REGULAR, FIBER_MPO_MTP_UPLINK, OTHER_REGULAR, OTHER_UPLINK. 

 

Figure 8

 

ETL_Staging_specification_pdf__page_27_of_36_.png


 

Note the following when importing network connection data:


1. The external items must be associated with equipment, and the association must be saved to the server, before the network connections can be synchronized.
2. If adding or updating information on a RELATION_ENDPOINT_PROPERTY row the corresponding CONFIGURATION_ITEM_RELATION must be marked 'new' or 'changed' in the staging-database.
3. Data for each of the five specific endpoint property types must specified for each relation endpoint property mentioned in the RELATION_END_PROPERTY table. 

Attachments
ETL integration examples.zip
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore