DCE sizing guide

Data Center Expert Virtual Appliance (VM)

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Data Center Expert
  • Data Center Expert Virtual Appliance (VM)
  • DCE sizing guide
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Data Center Expert Virtual Appliance (VM)
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
17189 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DCE sizing guide

Picard EcoStruxureIT
‎2019-11-20 06:13 AM

Last Updated: jdutra Cadet ‎2024-05-07 10:10 AM

This guide provides a starting point for sizing a new DCE solution.

 

If you set up DCE on a virtual machine, keep in mind that virtual environments run in a dynamic environment and need to be monitored and evaluated constantly. Adjustments are usually needed to ensure successful system performance.

 

For additional details on how to monitor and inspect the performance health of your DCE server, see the DCE performance troubleshooting guide.

 

Sensor updates calculation

 

When you size a DCE server, it is important to know the number of sensor updates per hour that the system will track. Sensor updates per hour is the number of sensors with values that change during one or more poll intervals over the course of an hour.

 

Calculating this value is not as simple as total number of sensors multiplied by the number of sensors in the system. Many devices have several sensors that do not change very often. If you calculate the rate of sensor change using the total sensor count, the result will be incorrectly inflated.

 

There are a few ways to more accurately approximate this value. To give you a starting point, we collected data from DCE systems that are connected to EcoStruxure and generated a data set from the connected devices. The average sensor quantity and the average rate of change per hour by device make and model are listed in the sensor updates calculator. You can use these reference values to calculate your sensor update per hour values.

 

For cases where you can’t use the reference document, you can use a small DCE deployment to measure the data, preferably with live devices deployed in their intended environment. Deploy a small DCE configuration and discover the device type in question. Then go to http://<dce server ip>/nbc/compress/support/sensorqstats. This page updates hourly and shows the amount of “processed” sensors for that hour. To get an accurate measurement, let the test run for a few hours, and then use the reported number as your update rate. Repeat this for the devices you want to profile.

 

Once you have all the data for each of your devices, add up the values. Remember, you want to calculate the sensor update quantity per hour for the entire system. Make sure you include virtual sensors if they will be used in the environment. Make sure you take your desired poll rate into account. You can drastically change your sensor update per hour value when you modify the poll period.

 

CPU and RAM sizing

 

Use the following characteristics to evaluate the CPU and RAM requirements for DCE server:

  • Device count
  • Sensor count
  • Sensor updates per hour

 

If your requirements are lower than all the listed requirements for a configuration size, use the CPU and RAM suggested values. If any of the three values are above the listed requirement, use the next largest configuration size.

 

Since sensor count and sensor updates per hour are often difficult to know before deployment, you can use the sensor updates calculator to see sample data gathered from DCEs deployed in the field. The guide contains average sensor count and average sensor updates per hour for some popular devices that DCE supports to help you determine estimated values.

 

It is important to note that operating with SNMPv3 comes with increased overhead and decreases the number of devices and sensors that a given DCE instance can monitor. The limits in the tables below assume using a specific protocol to manage the entire population (SNMPv1, Modbus, or SNMPv3). Mixed environments may see different upper limits for devices and sensors. These findings are based on testing against APC and Schneider Electric devices.

 

Basic Server Load

4 CPU / 4 GB of RAM    
  SNMPv1/Modbus SNMPv3
Device limits 500 125
Sensor updates per hour 45,000 11,250
Total sensors 67,000 16,750

 

Standard Server Load

8 CPU / 8 GB of RAM    
  SNMPv1/Modbus SNMPv3
Device limits 2000 500
Sensor updates per hour 180,000 45,000
Total sensors 270,000 67,500

 

Enterprise Server Load

16 CPU / 16GB of RAM    
  SNMPv1/Modbus SNMPv3
Device limits 4000 1000
Sensor updates per hour 360,000 90,000
Total sensors 540,000 135,000

 

For configurations that go above the limits for the Enterprise server load, consider splitting up the device load across multiple DCE servers. You can also contact technical support to review specific sizing requirements on a case by case basis.

 

Additional DCE variables that impact CPU and RAM sizing

 

There are other components in DCE to consider when you plan CPU and RAM sizing for your DCE virtual machine. These parameters vary widely, so exact guidance cannot be provided for all cases. The following activities and parameters have a direct impact on DCE performance. Depending on the extent of their use, additional modifications to the CPU and RAM may be needed.  

 

  • Thresholds
  • Virtual Sensors
  • API Integrations (DCO, Web Services, etc.)
  • Number of users logging into or logged into DCE thick client at same time
  • Graphing and reporting usage
  • Surveillance
  • Discovering a large number of devices in a short period of time 

 

If you plan to use these features, or you are concerned about their impact on system performance, you can review the details in the DCE performance troubleshooting guide.

 

Virtualization considerations for CPU and RAM sizing

 

All the sizing guidance provided assumes dedicated resources provisioned exclusively for the DCE virtual machine. In practice, unless you are using dedicated hypervisor for each DCE VM, it is likely that your DCE virtual machine will share a pool of resources with other virtual machines. The load of other virtual machines being serviced by the same CPU and RAM resources has the potential to directly impact the performance of your DCE. This is especially true when you start to overprovision CPU and RAM resources, which can then lead to increased latency and resource contention.

 

To better understand the health of your DCE virtual machine in its virtualization environment, use the resources in the DCE performance troubleshooting guide to analyze your system’s performance in real time and adjust the system accordingly.

 

Storage sizing

 

Successful deployment and operation of DCE relies on appropriately provisioned storage. There are two main components to appropriately size storage:

  • Performance
  • Disk capacity

 

Storage performance

 

The DCE virtual machine performs a write-heavy workload with high volumes of small I/O operations and is extremely sensitive to disk latency.

DCE latency events often appear as dropped sensor changes. This is reported by DCE in the nbc.xml log and is a good indication of storage contention issues. When making decisions about storage, choose a storage solution that is optimized for:

 

  • IO workloads that are 90% or more write-centric
  • Writes that are mainly 1k block aligned
  • Supporting <1ms latency for all read / write operations

 

With the above I/O pattern and latency requirements accounted for, the number of sensor updates per hour again comes into play to size the disk throughput appropriately. Use the following as guidance for how much storage throughput will be required. It is strongly encouraged that ALL of the following configurations use SSD drives.

 

Basic Server

  • Up to 45,000 sensor updates per hour
  • Requires 2MB/sec sustained write throughput

 

Standard Server

  • Up to 180,000 sensor updates per hour
  • Requires 8MB/sec sustained write throughput

 

Enterprise Server

  • Up to 360,000 sensor updates an hour
  • Requires 16MB/sec sustained write throughput
  • Storage caching of 1GB or larger

 

For configurations that go above the limits outlined in the Enterprise server load section, consider splitting up the device load across multiple DCE servers. You can contact technical support to review specific sizing requirements on a case by case basis.

 

Storage capacity

 

This is the recommended disk capacity deployment strategy:

  • Deploy the DCE OVA and DO NOT adjust the size of the initial hard drive.
  • Add a second drive to the virtual machine with a capacity of 250GB.
  • Monitor the Storage Repository usage in the DCE thick client and use the purge notification settings to alert you when data retention is nearing current capacity.
  • Add additional disks (never resize existing) to the DCE virtual machine in 250GB increments to meet data retention needs.

 

Additional DCE variables that impact storage performance

 

There are several DCE activities to take into consideration when you are sizing the DCE server. There are too many permutations of these variables to provide guidance on all of them. You can reference the DCE performance troubleshooting guide to better understand how to measure and tune this aspect of your system.

 

Variable activities that affect storage performance:

 

  • Other virtual machines using the network storage
  • Network latency
  • Disk latency
  • CPU latency
  • Virtual sensors
  • API Integrations (DCO, Web Services, etc.)
  • Number of users logging into or logged into the DCE thick client at same time
  • Graphing and reporting usage
  • Backup/Restore
  • Data purging
  • Surveillance 
  • Discovering a large quantity of devices in a short period of time

 

See  Surveillance deployments and Data Center Expert server performance

Attachments
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore