Alarms Service Methods

DCE web services API

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Data Center Expert
  • DCE web services API
  • Alarms Service Methods
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Sensor Service Methods
  • Device Service Methods
  • Device Groups Service Methods
  • Data Center Expert Web Services API
  • Alarms Service Methods
  • Sensor Service Methods
  • Device Service Methods
  • Device Groups Service Methods
  • Data Center Expert Web Services API
  • Alarms Service Methods

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to DCE web services API
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1373 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Alarms Service Methods

Picard EcoStruxureIT
‎2019-11-20 06:13 AM

Alarms Service WSDL

Alarms are conditions within the data center infrastructure that require attention. The textual contents of Data Center Expert alarms are localized to a user specified locale when they are retrieved from the server. If no locale is specified, the server default locale is assumed.

All alarms contain a reference to the device that is experiencing the alarm condition. If an alarm is associated with a specific device sensor, a reference to that sensor may also be included in the alarm. Sensor-related alarms are usually generated when a user-defined threshold for the sensor value is violated. Sensor thresholds can be defined either directly on the device or in the Data Center Expert server. 

An alarm is either active, meaning the condition that triggered the alarm still exists, or resolved, meaning the trigger condition no longer exists.

The following sections describe the methods of the Alarms service.

getAllActiveAlarms

Returns a list of ISXCAlarm objects that represent all alarms that are currently unresolved in the Data Center Expert server. 

Service: ISXCentralAlarmsService

Parameter Type Description
locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmByID

Returns an ISXCAlarm object that represents an alarm (active or resolved) in the Data Center Expert server and is identified by the specified ID. 

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier of an alarm that was created in the Data Center Expert server.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getActiveAlarmsForDevice

Returns a list of ISXCAlarm objects that represent active alarms associated with an DCE-server-monitored device which is identified by the specified ID. 

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier of a device that is being monitored by the Data Center Expert server.

excludeSensors (optional) boolean

When set to true, alarms associated with sensors will be filtered from the result set, and only alarms that are directly associated with the device will be returned.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getActiveAlarmsForSensor

Returns a list of ISXCAlarm objects that represent active alarms associated with an DCE-server-monitored sensor which is identified by the specified ID. 

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier of a sensor that is being monitored by the Data Center Expert server.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getActiveAlarmsForSeverity

Returns a list of ISXCAlarm objects that represent active alarms which have a severity that matches the specified severity level.

Service: ISXCentralAlarmsService

Parameter Type Description
severity ISXCAlarmSeverity

The severity to filter the resulting alarms on. 

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsHistory

Returns a list of ISXCAlarm objects that represent alarms that were active during the specified time frame.

Service: ISXCentralAlarmsService

Parameter Type Description
startDate xsd:datetime

The start date-time of the range to return data for. 

endDate xsd:datetime

The end date-time of the range to return data for. 

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsHistoryForDevice

Returns a list of ISXCAlarm objects that represent alarms that were active during the specified time frame and associated with the specific device.

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier for an DCE-server-monitored device. 

startDate xsd:datetime

The start date-time of the range to return data for. 

endDate xsd:datetime

The end date-time of the range to return data for. 

excludeSensors (optional) boolean

When set to true, alarms associated with sensors are excluded from the results, and only alarms directly associated with the specified device are returned.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsHistoryForSensnor

Returns a list of ISXCAlarm objects that represent alarms that were active during the specified time frame and associated with the specific sensor.

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier for an DCE-server-monitored sensor. 

startDate xsd:datetime

The start date-time of the range to return data for. 

endDate xsd:datetime

The end date-time of the range to return data for. 

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsHistoryForSeverity

Returns a list of ISXCAlarm objects that represent alarms that were active during the specified time frame and were of the specified severity.

Service: ISXCentralAlarmsService

Parameter Type Description
severity ISXCAlarmSeverity

The alarm severity to filter the results on. 

startDate xsd:datetime

The start date-time of the range to return data for. 

endDate xsd:datetime

The end date-time of the range to return data for. 

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsDeltaHistory

Returns a list of ISXCAlarm objects that represent alarms that had a change of status during the specified time frame.

Service: ISXCentralAlarmsService

Parameter Type Description
secondsInPast integer

The number of seconds to go back (relative to “now”) and evaluate alarm data for.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsDeltaHistoryForDevice

Returns a list of ISXCAlarm objects that represent alarms that had a change of status during the specified time frame and were associated with the specified device.

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier for an DCE-server-monitored device. 

 secondsInPast integer

The number of seconds to go back (relative to “now”) and evaluate alarm data for.

excludeSensors (optional) boolean

When set to true, alarms associated with sensors are excluded from the results, and only alarms directly associated with the specified device are returned.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsDeltaHistoryForSensor

Returns a list of ISXCAlarm objects that represent alarms that had a change of status during the specified time frame and were associated with the specified sensor.

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier for an DCE-server-monitored sensor. 

 secondsInPast integer

The number of seconds to go back (relative to “now”) and evaluate alarm data for.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

getAlarmsDeltaHistoryForSeverity

Returns a list of ISXCAlarm objects that represent alarms that had a change of status during the specified time frame and were of the specified severity.

Service: ISXCentralAlarmsService

Parameter Type Description
ISXCElementID String

The unique identifier for an DCE-server-monitored sensor. 

 secondsInPast integer

The number of seconds to go back (relative to “now”) and evaluate alarm data for.

locale (optional) String

Specifies the locale results are translated into before being returned. The default value is the locale configured in the Data Center Expert server.

setAcknowledgmentForAlarm

Allows the user to comment an alarm, set the alarm as hidden, and to suppress notifications of this alarm.

Service: ISXCentralAlarmsService

Parameter Type Description
alarmID String

The unique identifier for an alarm.

comment (optional) String

The comment the user wants to add to the alarm acknowledgment history.

 isAlarmHidden  boolean

Indicates if the alarm should be hidden in the DCE clients.

 isAlarmAlertSuppressed boolean

Indicates if the alarm notifications (alerts) should be suppressed.

getAcknowledgmentForAlarm

Allows the user retrieve the acknowledgments status: is alarm hidden, are alarm notifications suppressed.

Service: ISXCentralAlarmsService

Parameter Type Description
alarmID String

The unique identifier for an alarm.

getAcknowledgmentHistoryForAlarm

Allows the user to retrieve the acknowledgment history for an alarm.

Service: ISXCentralAlarmsService

Parameter Type Description
alarmID String

The unique identifier for an alarm.

deleteAcknowledgmentByID

Allows the user to delete alarm acknowledgment comments.

Service: ISXCentralAlarmsService

Parameter Type Description
 acknowledgmentID int

The unique identifier for an alarm acknowledgment.

alarmID String

The unique identifier for an alarm.

Attachments
ISXCentralAlarmsService_v2_0_360039287493.wsdl
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore