Using SpaceLogic SLA sensor to replace SHR humidity sensors
  • Using SpaceLogic SLA sensor to replace SHR humidity sensors
  • DavidChild
    DavidChild
Sisko DavidChild Sisko
‎2021-04-01 07:13 AM
Replacing a SHR humidity sensor when set as  4-20mA loop powered (2 wire).
Field Device
  • SHR100-T*
  • SpaceLogic SLA****
When replacing a SHR100-T* sensor, there are only 2 wires and the sensor is set to loop powered for measuring humidity.
The SLA sensor when used for measuring humidity and is only available as a 3 wire device when used with both 24Vac or 24Vdc (20-30Vdc) for measuring humidity, these are: power, ground and signal.
Either use a 3rd wire if available or use an alternative device.
Download the SpaceLogic Sensor Installation Sheet
  • Field Devices
  • DavidChild21
100% helpful (1/1)