Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Understanding Device Firmware Upgrade (DFU), “nosync,” and System Reliability

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Understanding Device Firmware Upgrade (DFU), “nosync,” and System Reliability
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Youghou_MOUMENE
    Youghou_MOUMENE

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
1378 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Understanding Device Firmware Upgrade (DFU), “nosync,” and System Reliability

Youghou_MOUMENE Troubleshooter
‎2025-09-28 05:58 PM

on ‎2025-09-28 05:58 PM

Issue

Maintaining device uptime and ensuring data integrity is critical. This article explains the Device Firmware Upgrade (DFU) process, the meaning of “nosync”, and how we’re enhancing system reliability.

Product Line

EcoStruxure Building Operation

Environment

EBO version 5.0, 6. and later

Cause

What Is “nosync”?

Introduced in SBO 1.5, the term “nosync” indicates an incomplete shutdown, which may result in data inconsistency. Devices in this state can be recovered using the DFU process.


What Is the DFU Process?

The Device Firmware Upgrade (DFU) process is a standardized recovery method that restores devices even when system data is corrupted—essentially reviving a “bricked” or “nosync” device.

Instead of booting from internal firmware, DFU allows the system to boot using data sent via USB.

Common use cases:

  • Downgrading to an earlier software version.
  • Recovering from failed shutdowns to restore functionality.

How Our Devices Store Data—and Why Proper Shutdowns Matter?

Unlike traditional computers, Automation Servers use eMMC memory for continuous data logging. The smallest writable unit is a 4096-byte block. To reduce wear, we use write caches that temporarily store data before writing it permanently.

A proper shutdown ensures all cached data is safely written. Interruptions can cause data loss due to:

  • Power Failure: If power is lost before the backup capacitor completes the write process.
  • Linux Kernel Crash: Prevents proper data management and shutdown.

Resolution

Improving System Reliability with EBO 7.0

In EBO 7.0 and later includes a major reliability enhancement. The Automation Server will now perform a smart check of its last shutdown status. If an improper shutdown is detected, the system automatically runs the Linux fsck (file system consistency check). This helps determine whether a “nosync” state is truly warranted, reducing false reports and improving reliability.

 

This enhancement has also been included in EBO versions 5.x and 6.x via hotfixes: 

  • EBO Hotfix 5.0.3.17009 (CP16)
  • EBO v6.0.4.10001 (CP8)

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • YoughourtaMoumene25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore