Satchwell MicroNet 100 Series LON Controllers Communicating with Automation Server (AS-P)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Satchwell MicroNet 100 Series LON Controllers Communicating with Automation Server (AS-P)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1422 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Satchwell MicroNet 100 Series LON Controllers Communicating with Automation Server (AS-P)

Gary Schneider Alumni (Retired)
‎2022-10-19 05:54 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-29 10:41 PM

Issue

Integrating a MicroNet 100 series LON controller/network into EcoStruxure Building Operation (EBO).

Product Line

Satchwell MicroNet

Environment

  • Satchwell MicroNet MNN-30-100
  • Satchwell MicroNet MNN-44-100
  • Satchwell MicroNet MNN-50-100
  • Satchwell MicroNet MNN-62-100
  • Satchwell MicroNet MNL-C

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

MicroNet 100 series LON networks are not natively supported in EcoStruxure Building Operation. Since the release of the MicroNet 50 series in 2008, support for MicroNet 100 series controllers with LON cards has been discontinued.

Resolution

Option 1: Use a Third-Party LON Management Tool

  • Bind MicroNet 100 series LON controllers to a standard LON network using tools like LonMaker® for Windows® (by Echelon).
  • Import the network into AS-P as a standard LON network.

Option 2: Convert to NCP Network

⚠️ Important: MicroNet NCP networks are not supported in EBO version 2022 (4.0) and later. This option is only viable for systems running EBO 3.x or earlier.

If using EBO 3.x or earlier:

  1. Remove LON Cards
    Detach LON cards from MicroNet 100 series controllers.

  2. Restore Jumpers
    Reconnect jumpers on the top two pairs of pins of the auxiliary card plug.

    Pins.jpg

  3. Replace Cabling
    Replace LON cabling with RS-485 compatible cable (e.g., Belden 8762 or equivalent).

  4. Reconfigure Controllers
    Use VisiSat to reprogram controllers for NCP communication.

  5. Import into AS-P
    Import the reconfigured network into AS-P under a MicroNet NCP interface.

  6. Touchscreen Limitation
    MicroNet LON touchscreens cannot be converted to NCP and must be removed.


Resources

  • MicroNet 100 Series Controller MLi's and Data Sheets
  • VisiSat 2.1 Build 196 – Software
  • VisiSat Release 2.1.196 Service Pack 1
  • VisiSat Release 2.1.196 Service Pack 2

Additional Notes

  • For systems running EBO 4.0 and later, Option 1 is the only viable integration path.
  • Ensure compatibility of cabling and controller firmware before conversion.
Labels (1)
Labels:
  • Satchwell MicroNet
Tags (2)
  • Find more articles tagged with:
  • CraigEllis25
  • GaryMontague22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore