Sample PE program that unlocks a group of doors at the push of a button
Select a Country
  • Sample PE program that unlocks a group of doors at the push of a button
  • AbeMeran
    AbeMeran
  • CraigEl
    CraigEl
AbeMeran Mentor
‎2024-04-19 10:22 AM
Last Updated: CraigEl Champion ‎2025-09-29 09:03 PM
How do I use a Plain English program to unlock a list of doors by toggling a switch?
Andover Continuum
  • NC2
  • ACX
  • Plain English
Customer request of a sample Plain English program to unlock a list of doors by toggling a switch.
This sample program is provided as a proof of concept only and is not intended as a complete solution but rather as a general guideline. Significant modifications may be required to adapt the sample program to an acceptable solution per local site requirements.
  • The sample program as written works with a "maintain position" toggle switch, if site is using a "momentary" switch then the program will need modifications.
Sample PE Program in PE EditorSample PE Program in PE Editor
See attached text file
DrUnlockButton.txt
Tags (5)
  • AbeMeran24
  • Doors
  • pe
  • program
  • sample