SP-MRDM firmware update fails with module's fault LED on
  • SP-MRDM firmware update fails with module's fault LED on
  • AbeMeran
    AbeMeran
Captain AbeMeran Captain
‎2024-08-12 06:52 PM
on ‎2024-08-12 06:52 PM
When attempting to update the firmware on the SP-MRDM module, the update process fails, and the module appears offline with the fault LED activated. A "Module not responding" error message is displayed that indicates the module should be disconnected, and a utility used to restore the firmware.
EcoStruxure Security Expert
  • SP-MRDM
  • SP-MRDM2
The module has lost its firmware during a failed firmware update attempt, leading to the offline status and fault LED activation.
To resolve this issue, follow these steps:
  1. Establish a connection to the SP-C controller using a web browser.
  2. Force a module update operation from the Application Software tab.
  3. Note that it may be necessary to check the "Skip Verification" checkbox during the update process.
  • EcoStruxure Security Expert
  • AbeMeran24
100% helpful (1/1)