SP-ACX on board inputs randomly activate/open on their own
  • SP-ACX on board inputs randomly activate/open on their own
  • AbeMeran
    AbeMeran
Captain AbeMeran Captain
‎2023-01-09 04:30 PM
on ‎2023-01-09 04:30 PM
One or more inputs on the SP-ACX will randomly report as open for a brief moment (a second or less), This can result in unauthorized door access if for example the input is associated with a door Exit Request.
EcoStruxure Security Expert
SP-ACX
Electrical noise in wiring
Increase the Alarm input speed, issue has been seen with Alarm input speed set to 0, increasing the input speed to 1 second typically resolves the problem.