Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Replacing a failed AC1 module under SP-AC1

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing a failed AC1 module under SP-AC1
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2838 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing a failed AC1 module under SP-AC1

AbeMeran Mentor
‎2022-01-19 03:09 PM

Last Updated: ContentModerator Explorer ‎2025-09-01 03:34 AM

Issue

What are the steps for replacing a failed AC1 or AC1Plus IO module hosted under SP-AC1 controller with available module either brand new or previously used?

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Controller
  • Continuum AC-1 IO Module
  • Security Expert Server

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Cause

Guidance needed on steps to replace a failed AC1/AC1Plus module hosted by SP-AC1 Security Expert controller

Resolution

While the recommended upgrade path is to replace any failed AC1 module with Security Expert IO module such as the SP-RDM2, it is possible to replace with same module type (AC1 or AC1Plus) using the steps below.

 

  1. Take note of the failed module address, this can be done either in the "Module addressing" window or by looking at the "Physical address" field in the Reader Expander.ModuleAddressing.jpg
  2. Using Continuum Cyberstation (or CX9900 Net Controller 1 with terminal interface) set the ID of the replacement module to the same as the ID of the failed module.
  3. Remove the failed module and put the replacement module in its place, once power is applied, the COMM LED of the replacement module should blink normally.
  4. Re-start the SP-AC1 controller, this can be done either by cycling power to the controller or by performing a re-start in the controller's web interface from a web browser.
  5. Once the controller is back online, from the client go to Sites\Controllers, right-click the appropriate controller, and select "Module addressing", in the module addressing window you should see the failed module offline and registered, the replacement module should also be present using the same ID as the failed module but offline and NOT registered.
  6. Click on "Update modules"UpdateModules.jpg
  7. After the system displays "Update module command sent OK" wait a minute, then bring up the "Module addressing" window once again, the failed module should now be gone and the replacement module should now be online and registered. You should also see an entry in the "Status page view" for each module indicating the module has registered successfully.ModuleRegistered.jpg
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (5)
  • Find more articles tagged with:
  • AbeMeran22
  • ac1
  • ac1plus
  • failed
  • io
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore