Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Issue
Need to replace an AVUE, AVUX or AVUM Mark 5 Actuator
Product Line
Field Devices
Environment
- AVUE5305
- AVUE5355
- AVUE5304
- AVUE5354
- AVUX5202
- AVUM5601
Cause
Need to find a replacement for the obsolete AVUE, AVUX or AVUM Mark 5 actuator, that will allow the valve to be retained.
Resolution
The AVU* Mark 5 range of actuators can be replaced from the MZ300S range.
- AVUE5305 replace with MZ300S-24M
- AVUE5355 replace with MZ300S-24M
- AVUE5304 replace with MZ300S-24M
- AVUE5354 replace with MZ300S-24M
- AVUX5202 replace with MZ300S-24F
- AVUM5601 replace with MZ300S-230F
The AVUE, AVUX, AVUM Mk 5 Datasheet is attached
MZ300S-24M Installation Instructions
MZ300S-24F Installation Instructions