Issue
Need to replace an AVUE, AVUX or AVUM Mark 5 Actuator
Product Line
Field Devices
Environment
- AVUE5305
- AVUE5355
- AVUE5304
- AVUE5354
- AVUX5202
- AVUM5601
Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Cause
Need to find a replacement for the obsolete AVUE, AVUX or AVUM Mark 5 actuator, that will allow the valve to be retained.
Resolution
The AVU* Mark 5 range of actuators can be replaced from the MZ300S range.
- AVUE5305 replace with MZ300S-24M
- AVUE5355 replace with MZ300S-24M
- AVUE5304 replace with MZ300S-24M
- AVUE5354 replace with MZ300S-24M
- AVUX5202 replace with MZ300S-24F
- AVUM5601 replace with MZ300S-230F
The AVUE, AVUX, AVUM Mk 5 Datasheet is attached
MZ300S-24M Installation Instructions
MZ300S-24F Installation Instructions