RP-C Floating 0–10Vdc Outputs
  • RP-C Floating 0–10Vdc Outputs
  • DavidChild
    DavidChild
  • Gary
    Gary
Gary Schneider Alumni (Retired)
‎2021-04-21 08:04 AM
Last Updated: Sisko DavidChild Sisko ‎2021-04-22 04:20 AM
The 0–10 measured output voltage from the RP-C’s Ub terminals may not provide the expected voltage.
SmartX Controller RP-C
On the RP-C controller's the Ub return terminals although internally connected to each other are isolated from ground (-).
Add a ground reference connection between ground and one of the return terminals of the controller.
Example if the controller is stand-a-lone using terminal 3, which is an isolated terminal and can be used for the connection.
  • GaryMontague21