Issue
How is a Pulse Digital Output (BACnet Binary Output) created via a Continuum Conversion
Product Line
EcoStruxure Building Operation
Environment
- b3 Controller
- Infinet Controller
- Continuum Conversion
Cause
A Continuum Infinet Output created as Elec Type Digital has Format $###, as below
When this is converted to EBO, a Type "BACnet Digital Output (Continuum) binary-output" is created.
Resolution
The Format needs to be modified to ###.### or #.###, as below
The BACnet binary output created in the conversion will now be a "Digital Pulsed Output"
Summary below