Number of wires in a RP-C terminal
  • Number of wires in a RP-C terminal
Gary Schneider Alumni (Retired)
‎2023-06-06 02:44 AM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:32 AM
Page 1031 of the hardware reference guide only states wire cross-sectional area: 0.34 to 2.5 mm2 (22 to 14 AWG) and not the number of wires allowed to terminate.
  • Building Operation Room Controller (RPC) 24V
  • Building Operation Room Controller (RPC) 230V
Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
Documentation clarification.
It is OK to terminate up to 2 wires into each terminal as long as the total area of the wires does not exceed 2.5mm2.