Network Port Scanning causes Continuum controller to fail

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Network Port Scanning causes Continuum controller to fail
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
587 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Network Port Scanning causes Continuum controller to fail

Captain AbeMeran Captain
‎2024-10-16 09:11 AM

on ‎2024-10-16 09:11 AM

Issue

Continuum NetController fails when a port scanning tool runs a network port scan on the ethernet network where the controller is connected.

Some of the controller failures that have been reported to Product Support Services include controller scan locked, controller resetting, hanged, stuck in bootloader etc. In some cases the controller may be running but exhibiting very strange symptoms due to its tasks scheduling being disturbed by the scanning traffic and/or due to memory corruption.

Product Line

 Andover Continuum

 

Environment

  • Continuum CX Gen 1
  • Continuum Net Controller II
  • Continuum ACX 2 Controller
  • Continuum ACX 4 Controller
  • Continuum bCX4040 (BACnet)
  • Continuum bCX4000 (Router)
  • Continuum bCX9640 (Infinet)

 

Cause

The legacy Continuum controller's network stack is not able to handle some of the packets generated by network scanning tools, most such tools explicitly point out that older internal systems may not be able to handle the port scanning traffic and may fail during the process.

 The controller error log may show some variation of the following errors...

 

219 I 08/10/2024 13:14:53.35 0xbadd0018 0x00002500 0x001783f0 0x40602004 0x0017eeb4
Reset (Spurious interrupt)

 

4914 I 09/14/2022 09:00:54.00 0xbadd0002 0x00002600 0x02001bd4 0x48082600 0x020ffbb8
Reset (access error)

Resolution

The Continuum NetControllers are now legacy systems no longer in active development, therefore, the only known solution is to add  the controller's IP address to the tools white list so that no port scanning packets are directed to the controller.

 

It is important to note that NONE of the Continuum NetControllers listed above use Windows or Linux based OS, this makes them less vulnerable to the typical hacker attacks. 

 

Andover Continuum is a legacy Schneider Electric product. We strongly encourage upgrading your system to the more secure and feature-rich platform, EcoStruxure Building Operation. 

Labels (1)
Labels:
  • Andover Continuum
Tags (6)
  • Find more articles tagged with:
  • 0xbadd
  • AbeMeran24
  • badd
  • port
  • port scanning
  • scan
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of