Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
Issue
Why is it recommended to not mix high and low voltage connections on the same side of an CRS-HH-REL-10?
Product Line
EcoStruxure Building Operation.
Environment
- Building Operation Room Controller (RPC) 24 V
- Building Operation Room Controller (RPC) 230 V
Cause
According to the documentation, it is not recommended to mix high and low voltage connections on the same side of the device.
Resolution
There must be a minimum distance between terminals connected to High Voltage and terminals connected to Low Voltage of at least 5.5 mm to prevent the chance of voltage creep between the terminals.