MicroNet and IAC Time and Holiday Schedules not functioning after upgrading from SBO to EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MicroNet and IAC Time and Holiday Schedules not functioning after upgrading from SBO to EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
883 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MicroNet and IAC Time and Holiday Schedules not functioning after upgrading from SBO to EBO

Gary Schneider Alumni (Retired)
‎2021-06-29 08:27 AM

on ‎2021-06-29 08:27 AM


Issue

After upgrading a site that contains MicroNet or IAC controllers from SBO to EBO the time Schedules no longer display time periods entered.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation (from v2.0.1)
  • Building Operation WebStation (from v2.0.1)
  • Building Operation Enterprise server (from version 2.0.1)
  • Building Operation Automation Server (AS Classic from v2.0.1 to v3.1 and AS-P from v2.0.1)

Cause

From EBO 2.0.1 release includes support for MicroNet time and holiday schedules in WebStation, to achieve this the existing SBO schedules have been replaced by a TGML graphic for both WebStation and WorkStation.

Resolution

To enable the new schedules, run the Data Importer on each MicroNet interface, this will add new TGML schedule objects for all existing MicroNet and IAC Time and Holiday schedules.

Before upgrading.
1 SBO 1.9.4.29.jpg

After upgrading.
2 EBO 3.1.2.29 after Upgrade.jpg

Carry out a Data import.

3 EBO 3.1.2.29 Data Import.jpg

After the Data import, then the associated TGML graphics can be seen.

4 EBO 3.1.2.29 After Data Import.jpg

Further information is available in the EBO 2.0.1 release note.

The graphic creation is confirmed in the trace information presented when Data importing:

The trace will be sent to: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation n.n\DataImport\Trace.DataImport.MicroNet Interface.txt and the following is seen:

Source: C:\Satchwell\Projects

Full URL: C:\Satchwell\Projects

Processing XML...

Committing to server...

Creating object editor graphics (3) ...

Object editor graphics created

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
Tags (1)
  • Find more articles tagged with:
  • GaryMontague21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore