Lock path of binding point does not work
Select a Country
  • Lock path of binding point does not work
  • DavidChild
    DavidChild
  • PeterEdvik
    PeterEdvik
PeterEdvik Champion
‎2020-03-19 02:40 AM
Last Updated: DavidChild Champion ‎2020-03-19 02:41 AM
When trying to lock the path of a binding point, the path doesn't change.
Right clicking on a binding path to lock the pathRight clicking on a binding path to lock the path
The locked symbol appears (1), but nothing happens to the path (2).
1. The path is unchanged. 2. The lock symbol is displayed1. The path is unchanged. 2. The lock symbol is displayed
When trying to save the changes the locked symbol (1) disappears.
Building Operation Workstation v. 3.0
Lock Path is not converting the relative path to an absolute path hence the save is not working as expected. This works fine in version 2.0 and is fixed in version 3.1.
  1. Upgrade to version 3.1 where this problem is fixed.
  2. In version 3.0 the path can be manually updated to the correct locked path before saving.
    Manually updated binding path to a correct locked pathManually updated binding path to a correct locked path
    In the example above the path to the Analog Value in the binding point is
    /Server 1/test/Analog Value
    Therefore the correct locked path should be
    ~/test/Analog Value/Value
    Make sure you have locked the path before saving.
Tags (2)
  • PeterEdvik20
  • QC 42192
0% helpful (0/2)