Licensing Settings error: Failed to get current data from server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Licensing Settings error: Failed to get current data from server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • PeterEdvik
    PeterEdvik

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1972 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Licensing Settings error: Failed to get current data from server

Janeway PeterEdvik Janeway
‎2020-03-18 02:27 AM

Last Updated: Sisko DavidChild Sisko ‎2020-03-18 02:28 AM

Issue

Error message when trying to edit the Licensing Settings for an Automation Server in Device Administrator.

LicensingSettingsBlur.png

Error message:

Failed to get current data from server: Error when attempting to get license information: :Request to [AS-IP-ADDR]:443 failed. [SSL: CERTIFICATE_VERIFY_FAILED] certificate verify failed (_ssl.c:833)

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Automation Server

Cause

The Server has been added with EBO server protocol HTTPS, but no SSL certificate has been transferred to the server.

The error message is displayed after taking the following steps:

  1. In Building Operation Device Administrator check Show licenses
  2. Select an Automation Server by checking the box in front of the question mark displayed instead of the server name
  3. Click License Settings

LicenseAdministrator.png

Resolution

This problem can be resolved either by adding a SSL Certificate to the server, or by changing the connection type to HTTP.

Solution I: Adding an SSL Certificate to the server

  1. Click the server name in Device Administrator. (The server name will be a question mark as DA will not be able to communicate with the AS in this state.)
  2. Select SSL Certificate in the left menu and click Generate new certificate.
  3. Click OK if you agree to use an auto-generated password. (Otherwise click Cancel enter a password and click Generate new certificate again)
  4. Click OK
  5. Click Transfer to server
  6. Click OK
  7. Go back to the server list and verify that the State says Ready and that the name is displayed correctly.

Solution II: Changing connection type to HTTP

  1. Remove the server from the Device Administrator
    1. Uncheck Show licenses if it is selected
    2. Select the server by checking the box in front of the question mark displayed instead of the server name
    3. Click Remove in the green bar above the server list
    4. Confirm by clicking Yes
  2. Add the server with connection type HTTP
    1. Click Add Server
    2. Enter the server address, password and choose HTTP as EBO server protocol
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • PeterEdvik20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore