Insight Sensor/Multi sensor Ambient Light Sensor Calibration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Insight Sensor/Multi sensor Ambient Light Sensor Calibration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3520 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Insight Sensor/Multi sensor Ambient Light Sensor Calibration

Kirk MikaelKrantz Kirk
‎2023-11-29 04:43 PM

on ‎2023-11-29 04:43 PM

Issue

The Insight Sensor and Multi Sensor Ambient Light Sensor require calibration before they can be effectively used.

Product Line

EcoStruxure Building Operation.

Environment

  • Insight Sensor.
  • Multi Sensor

Cause

When setting up a new Insight Sensor or Multi Sensor device, the default settings for Gain and offset may result in inaccurate readings. Calibration is necessary to ensure accurate data collection based on the specific installation area.

Resolution

To perform the calibration, the following two tasks need to be carried out manually:
  1. Calibrate the Light Sensor:
    • Conduct the calibration process in an environment without any daylight for optimal results.
    • Set the light to 100%.
    • Measure the lux level at the reference point using a lux meter.
    • Adjust the gain settings on the sensor to match the measured lux level.
  2. Linearize the Feedback Signal:
    • In some cases, lights may not provide a linear feedback (lux level) as the output increases.
    • To compensate for this non-linearity, the signal from the controller is linearized before being sent to the output.

During the optimization phase, the controller incrementally increases the output in 10% steps, measuring the adjacent lux levels for each step. The maximum lux supplement is calculated by subtracting the lux level at 100% output from the lux level at 0% output.


After the optimization phase, breakpoints are determined and verified by re-running the test. If the results fall within the maximum difference limit compared to a linear signal, the calibration test is considered valid.


Remember, performing the calibration process without any daylight present will yield the best results.

 

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • MikaelKrantz23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore