Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Infinet to MP or RP controller communications

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Infinet to MP or RP controller communications
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1986 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Infinet to MP or RP controller communications

Dave_Shore Schneider Alumni (Retired)
‎2021-07-23 07:39 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:57 AM

Issue

Infinet to MP or RP controller communications

Product Line

EcoStruxure Building Operation

Environment

  • Infinet Controller i2 i1
  • SmartX IP RPC RP-C, MPC, MP-C, MPV, MP-V Controller

Cause

The power cycle and bandwidth requirements need to be considered when setting the parameters for Infinet to MP/RP communication

Resolution

First ensure a good understanding of "Infinet Under the hood" article.

A direct binding can easily be made between an Infinet controller object like an Analog Value and an MP/RP Controller object like an Analog Value.

The whole communication path is not BACnet so a "Value transfer settings" window can be opened that controls part of the EBO communication process.

This default configuration (Infinet to MP/RP) will usually result in the Infinet Value being collected every 10 seconds, this value will then only only be written to the MP/RP when the value changes. To ensure the value is correct following a power cycle either enable Guaranteed transfer and set to 1 minute, or use the retailed level on the MP/RP object

 

If there is a listview, graphic or watch window containing the Infinet Object, this causes the value to be collected every 500mS, as seen in the screenshot below

2021-07-22_16-09-51 2.jpg

 

If the Infinet Object is "exported", (see "Infinet under the hood" for details) then the communication can be much more efficient as the values are only sent when there is a change (greater than the object threshold for analog inputs).

 

If the communication is from the MP/RP Object to the Infinet controller Object, then a BACnet COV subscription will be set up by the EBO server to the MP/RP Controller, this will be renewed if either is reset/power cycled.

It needs to be remembered that the "Value Transfer settings" is an EBO property and in this case the communication is controlled by the EBO Server with Infinet in one direction and BACnet in the other. So the communication to the MP'/RP controllers will either be a write or a COV subscription from the EBO Server.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidShore21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore