How to obtain i2/b3 device's model from the controller's perspective

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to obtain i2/b3 device's model from the controller's perspective
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3472 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to obtain i2/b3 device's model from the controller's perspective

Captain AbeMeran Captain
‎2024-08-22 05:43 PM

Issue

In Andover Continuum, the model name of a field device (i2/b3) is always obtained from the SQL database as there is no direct way to retrieve the model directly from the controller. Consequently, discrepancies between the model stored in the SQL database and the actual controller may lead to uprev errors like "This Uprev file does not match this type of controller"

 

i2800-2.PNG 

In the screenshot above, note that both the device's editor as well as the command line, report the controller's model as i2800, when in fact the hardware associated with the device is an i2920.

 

Note: In EcoStruxure Building Operations, where a distributed database design is employed, the device's model type is always obtained from the proxy representing the device in the Automation Server.

Product Line

Andover Continuum

Environment

  • All i2s
  • All b3s

Cause

Frequent model mismatches for i2/b3 devices in Continuum installations often result in errors when attempting to upgrade the device's firmware.

Resolution

To obtain the device's model (controller type) from the Continuum controller hosting the device follow the steps below:

  1. In the master controller, create an InfinityNumeric, in this example we will name it 'DevModel'
  2. In the master controller, create an InfinityProgram, in this example we will name it 'GetDeviceModel'
  3. Enter the following lines of code in the program...
DevModel = <device_name> CntrlType

Stop

***Replace <device_name> with your i2/b3 device's name

 

i2800-4.PNG

Note in the screen capture above, that the program reports the actual device's model to be i2920.

The mismatch needs to be corrected by either installing the correct hardware or adjusting the model in the device editor in Cyberstation to align with the hardware.

 

IMPORTANT

If the program reports the model as 0 (zero) it means the proxy representing the device in the master controller has lost the model number, you will need to reload the whole master controller to recover, make sure to select the option to reload the controller but NOT its children.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • AbeMeran24
  • AbeMeran25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore