Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Hosting a third party BACnet device on Multiple Automation Servers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Hosting a third party BACnet device on Multiple Automation Servers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1517 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Hosting a third party BACnet device on Multiple Automation Servers

Guinan MikaelKrantz Guinan
‎2024-11-19 06:02 AM

on ‎2024-11-19 06:02 AM

 

Issue

Is it possible to host the same third party BACnet device on the AS-P private networks on multiple automation servers, which are all connected on the same network?

Product Line

EcoStruxure Building Operation.

Environment

Building Operation Automation Server Premium

Cause

The design in question is a 3-storey accommodation building which includes 1 x BMS panel/AS-P per level. However, only 1 x Mitsubishi EW-50E BACnet gateway is being provided for the building.

Resolution

It is possible to host the same 3rd party BACnet device in multiple AS-Ps. Some caution is required, however, because if the user makes changes to an object in that device through one AS-P, that change may not be reflected in other AS-Ps.

When viewing runtime variables, such as 'Value' and 'Status Flags', this is not a problem because the EBO server will always get new values from the wire. Where the problem can present itself, is when changes are made to configuration values because these are only updated in an EBO server during an upload operation.

For example, if you set the hi-limit and low-limit values in an analog-value object from one AS-P, those values will not be updated in other AS-Ps until you do an upload of that object.

 

The other place where this problem may present itself is in schedules. An EBO schedule only writes values to a device when that value changes. For example, if you have a schedule configured to change the setpoint to 65 degrees at 5pm, EBO will only write a value of 65 if the current 'local' value is not 65. If this schedule only writes 1 time per day and someone has set the value to 70 from another AS-P, the first AS-P does not realize the value has changed so that schedule will not generate a write request to set the value to 65 (it will stay at 70). However, if you have a program or trend-log monitoring the value, the AS-P will be tracking that value and realize it is not 65 so you will see a write request at the scheduled time.

 

The system works this way because reading all values of all devices and all objects all the time is simply not practical. As long as the user is aware of how the system is designed, they can avoid these potential issues.

 

Make sure to use Static IP, so IP do not change, or you get multiple DHCP servers on the same network.

 

Another alternative is to host the BACnet device in one AS-P only, then using internal bindings to share the data with other AS-Ps.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • MikaelKrantz24
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore