Issue
ACX57xx Continuum controller frequently reboots itself, loses configuration and/or stop granting access to doors until reloaded.
In the controller error log frequent and spontaneous re-starts of the controller can be observed without an apparent cause such as power failure for example.
Here is another error log from different controller with same issue, a similar signature can be observed in the following screen shot
Product Line
Andover Continuum
Environment
Continuum ACX 2 Controller
Continuum ACX 4 Controller
Cause
Electrical noise coming from door striker corrupting controller's memory.
Resolution
An external Varistor may be installed for Noise Suppression of a Door Strike. Here is a link to a part that may be used for this purpose:
The part should be installed at the Door Strike, from the switched 24VDC terminal to the common 24VDC terminal, like this: