EasyLogic CP Series Differential Wet Pressure Transmitters Ports
  • EasyLogic CP Series Differential Wet Pressure Transmitters Ports
  • MikaelKrantz
    MikaelKrantz
Guinan MikaelKrantz Guinan
‎2025-09-23 06:18 PM
on ‎2025-09-23 06:18 PM
Which port (P1 or P2) should be connected to the high and low pressure?
Field Devices.
EasyLogic CP Series Differential Wet Pressure Transmitter (CP-LI-DP-TR-xxxx)
The product documentation does not clearly specify which port corresponds to the high-pressure side and which to the low-pressure side.
P2 is the high-pressure port.
P1 is the low-pressure port.
  • Field Devices
  • MikaelKrantz25