EBO-RP-C fails to download Modbus points with HMI Control Mode

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EBO-RP-C fails to download Modbus points with HMI Control Mode
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Youghou_MOUMENE
    Youghou_MOUMENE

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
485 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EBO-RP-C fails to download Modbus points with HMI Control Mode

Lt. Commander Youghou_MOUMENE Lt. Commander
‎2025-07-28 08:50 AM

on ‎2025-07-28 08:50 AM

 

Issue

RP-C contains 2 Modbus devices of the same type on the Modbus interface, one of the Modbus devices reports error 'Value Invalid reference type for HMI' when points with HMI as control mode are downloaded.

Fejl download RP-C.png

 


 

 

Product Line

EcoStruxure Building Operation

Environment

  • Detected in version EBO 6.0.3.112 and above

Cause

Modbus point with Control Mode set to HMI will fail to download to RP-C if its reference is invalid.

  1. Create a folder in an RP Application folder called 'Test 1'.
  2. Create an Analog Value object in the ‘Test 1’ folder.
  3. Create a Modbus Device and add a Modbus Analog Output Point to it.

    EngYoug086_2-1751572668823.png

  4. Click on the gear to the right of the ‘Value’ property in the new ‘Modbus Analog Output Point’ and reference the Analog Value/Value from step 2.
  5. Set the ‘Control mode’ of the ‘Modbus Analog Output Point’ to HMI.

    EngYoug086_5-1751574394600.png

     

  6. Edit the reference from step 2. so that it manually looks for ‘Test 2’. A warning appears indicating that the reference is invalid and Control mode is automatically set back to ‘Write only’.

    EngYoug086_6-1751574635864.png

  7. Change the ‘Control mode’ back to ‘HMI’ and Save, the system displays 'Value Invalid reference type for HMI' error.

    EngYoug086_7-1751574887563.png

     

Resolution

A valid reference must be defined to a Modbus point with control mode set to HMI so that it can be downloaded to RP-C.

 

From step 4. set the reference back to a valid one ' Test1/Analog Value/Value ' and download the object to RP-C.

EngYoug086_8-1751575985450.png

 



Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • Youghou_MOUMENE25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore