Detector Showing Device Internal Trouble
Select a Country
  • Detector Showing Device Internal Trouble
Sandeep_Kumar006 Troubleshooter
‎2025-06-23 05:40 PM
Last Updated: ContentModerator Explorer ‎2025-09-01 03:31 AM
Detector showing internal trouble.
ESMI Fire Detection.
  • FFSULH2001.
  • FFSULH2003.
Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
If the analogue value of a detector measured by the panel is outside of the normal operating range (≤41 to ≥95) the panel will show “Internal Trouble” indicating that the detector is faulty and should be serviced.
Replace the faulty detector.
  • ESMI Fire Detection
  • SandeepKumar25