Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Debugging MP and RP controllers Modbus RTU

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Debugging MP and RP controllers Modbus RTU
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2629 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Debugging MP and RP controllers Modbus RTU

Sisko DavidChild Sisko
‎2022-02-08 04:55 AM

Last Updated: Picard David_Purser Picard ‎2024-11-20 09:54 AM

Issue

Debugging SpaceLogic MP and RP controllers Modbus RTU

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller (RP-C)
  • Building Operation RP-V VAV
  • Building Operation EZLogic RP-C
  • Building Operation EZLogic RP-V

Cause

There is no packet data can be logged or viewed for Modbus MP and RP controllers and RP controller has no transmit and receive LEDs for the Modbus and no packet data can be logged or viewed. Article Modbus in the MP and RP Controller Introduction provides information on the differences between the Automation Server and MP and RP controllers Modbus operations.

Resolution

There are a couple of options, but they involve using another device connected to the Modbus network to view the packets

  • Use a PC based Modbus slave simulator
  • Use an Automation Server set up as a Modbus RTU slave, the packets can be sent to the trace log then viewed in the usual way. 
    Note: A defect with v3.2.1 EBO means this solution cannot be used to monitor a Modbus RTU bus because the AS replies to all requests and may cause conflicts on the network. All versions 3.1.2 and earlier work fine, as well the EBO 2022 (v4.0.1) as detailed in the Known Issue Modbus Slave incorrect response
  • Can use Picoscope to perform Serial Decoding for Modbus RTU as detailed in Picoscope Configuration for Modbus RTU capturing and decoding
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • DavidChild22
  • DavidShore22
  • PeterLarsen22
  • PeterLarsen23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of