Issue
When changing values like Check-in interval (s) under Poll Control for Zigbee device SED-MTH-G-5045, the value seams not to have been change when opening the dialog again.
Product Line
EcoStruxure Building Operation.
Environment
- Building Operation Automation Server Premium (AS-P)
- Building Operation Room Controller (RP-C)
- non-Greenpower sensors SED-MTH-G-5045
Cause
Setting is sent to the sensor only once every tenth minute.
Resolution
Open the dialog box again after 10 minutes to verify your changes.