Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Conversion of Continuum devices from i2 to b3 (and vice-versa) in the field using RoamIO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Conversion of Continuum devices from i2 to b3 (and vice-versa) in the field using RoamIO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4807 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Conversion of Continuum devices from i2 to b3 (and vice-versa) in the field using RoamIO

AbeMeran Mentor
‎2023-08-14 05:13 PM

Issue

Currently, a procedure exists to do conversion of i2 to b3 and vice versa using Continuum Cyberstation and NetControllers.

 

However, it is much simpler to do the conversion using the RoamIO and the Infinet/BACnet Service Tools.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Continuum i2 Controllers (except -V)
  • Continuum b3 Controller (except -V)

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

This article describes an alternate and simplified conversion method to the original procedure published to convert i2 to b3.

Before using this procedure, read the Conversion of Continuum devices from i2 to b3 and vice-versa in the field Knowledge Base article in its entirety for important information about converting i2/b3 controllers in the field. 

Resolution

IMPORTANT NOTE

If the device you are converting is of model i2/b3 865/866/885 STOP

First confirm that the device is NOT a -V device, this is accomplished by inspecting its version number, -V devices have a "1" embedded in the second part (after the ".") of the version number

 

A -v device will show the version number as follows...

3.501027

A non -v device will show the version number as follows...

3.500027

 

Before starting the procedure, you need the following items:

  • The device to be converted.
  • The serial number of the device to be converted.
  • A RoamIO2 configured to communicate with your PC via Bluetooth and the Infinet and BACnet Service Tools
  • A special, firmware application upgrade file for the appropriate device model as provided by Product Support
  • A bootloader file for the appropriate device model, provided by Product Support

To convert i2 field devices into b3 BACnet using RoamIO2

  1. Contact Product Support and request the conversion files for the specific model(s) you
    wish to convert.
    You will be provided with an application file (e.g. i2920toB3920B4.500077.upd) and a boot loader file (e.g. B3920BootB4.500077.upd) for each model you are converting.
  2. Connect the RoamIO2 directly to the i2 device (make sure device is disconnected from field bus)
  3. Launch the InfinetServiceToolPC.exe (attached) and click on the connect icon
  4. Once the device shows up on the tree, right click on it then select 'Uprev firmware...'
  5. i2deviceInTree.PNG
  6. Send the conversion application file provided by Product Support
  7. Convert1.PNG
  8. Once the uprev operation is complete, click the connect icon to disconnect the Infinet Service Tool from the i2 device then close the InfinetServiceTool app.
  9. Cycle power to the RoamIO2 then start the BACnet Service Tool
  10. In the BACnet Service Tool, de-select View by networks, then click the connect icon, the conversion from i2 to a b3 causes the device to default to baud 38400 and an invalid BACnet master MAC id, so upon connection the following error will be shown...
  11. RoamIoBaudNotFound.PNG
  12. Click 'Yes' to continue
  13. From the 'Tools' menu select 'Set b3 baud rate' and set it to Baud38400
  14. RoamIoSetBaud.PNG
  15.  From the 'Tools' menu select 'Set offline b3 MAC id' and enter the serial number of the device and a valid MAC id then click on 'Apply'
  16. RoamIoModifyMacID.PNG
  17. If the baud and MAC id have been set successfully, the device will automatically pop up in the tree but it will only be partially online, to bring the device fully online, click the red disconnect icon on the BACnet Service Tool to disconnect from the device, wait about 30 seconds then  click the now green connect icon to reconnect the BACnet Service Tool to the device
  18. Right click on the device then select 'Update OS', send it the appropriate boot loader file provided by Product Support
  19. SendBoot.PNG
  20. Once the uprev of the boot loader has completed, select the device and click on 'Cold start device'
  21. After the device re-start, click on the device in the tree and select 'Switch view', confirm the firmware and boot loader versions are correct. (you may need to do a refresh from the 'Tools' menu)
  22. BootVersion.PNG
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
InfinetServiceToolPC_2000996.zip
Tags (2)
  • Find more articles tagged with:
  • AbeMeran23
  • AbeMeran26
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore