Collecting String data from third party BACnet systems
  • Collecting String data from third party BACnet systems
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
Dave_Shore Schneider Alumni (Retired)
‎2019-07-08 07:28 AM
Last Updated: Administrator DavidFisher Administrator ‎2019-08-06 02:15 PM
Collecting String data from third party BACnet systems where they do not support BACnet String Objects
  • Third Party BACnet systems
  • Continuum Text/Strings Datetime
BACnet String and Date (characterstring-value and datetime-value) objects are not included in some BACnet systems eg. Continuum.
Continuum supports these objects types in a proprietary manor but not as BACnet objects, therefore these values cannot be simply collected by EBO
A simple method of collecting text strings from Continuum is to convert each character to its ASCII equivalent number, then pass these values via BACnet Analog Values, then convert back to a string in EBO
The simplistic PE program below shows conversion of the first 8 characters of "String8Character" Object to 8 Analog Values "StringChr01-08", these are collected by EBO
The Script Program below converts the Analog Values back to a Text String
Labels (2)
  • DavidShore19