Capture a Sigma trace log in EBO/SBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Capture a Sigma trace log in EBO/SBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1216 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Capture a Sigma trace log in EBO/SBO

Sisko DavidChild Sisko
‎2021-08-02 01:12 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:56 AM

Issue

  • How to troubleshoot a communication issue with the Sigma interface
  • Is there a log available within the ES that shows the Sigma communication between Sigma controllers and the ES

Product Line

EcoStruxure Building Operation, Sigma

Environment

  • Building Operation Workstation
  • Building Operation Enterprise Server

Cause

When troubleshooting Sigma issues in an ES it can be helpful to see the communication between the Sigma controller and the Sigma interface in the ES to help identify this issue. The trace log within the ES is available and is configured as described below in the resolution.

Resolution

The level of logging for Sigma in the Trace Log needs to be increased:

  1. Open Workstation and navigate to [ES name]/System/Modules/Trace/Loggers/nsp/nsp.pin.
  2. Right-click "nsp.pin.sigma" and choose Properties.
  3. Under Level, change from "Information" to "Trace", then click ok.
  4. Let it run a few minutes. If there are some user input needed to recreate the Sigma issue, then perform these steps now. e.g. If ifs a graphics issue then run the respective graphic.
  5. Retrieve the log by right-clicking [ES name]/System/Modules/Trace/TraceSettings and choose Trace settings->Get trace log. 
  6. Save the log file.
  7. A useful tool available on the Community, the Sigma decoder can be used to assist in viewing/debugging the Sigma trace log file information saved in the previous step.
  8. Once debugging is complete remember to change log level back to "Information" (reverse of step 3).

 

Note: If the ES is restarted for any reason whether by manually stopping in the Software Administrator or other, the nsp.pin.sigma will default back to 'Information'.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • DavidChild21
  • DavidChild22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore