Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet devices not found but are visible in other applications

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet devices not found but are visible in other applications
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Dave_Shore
    Dave_Shore

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5549 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet devices not found but are visible in other applications

Dave_Shore Schneider Alumni (Retired)
‎2020-06-19 06:01 AM

Last Updated: Sisko DavidChild Sisko ‎2020-06-19 06:01 AM

Issue

BACnet devices not found but are visible in other third party BACnet applications

An update may cause devices to go offline

Product Line

EcoStruxure Building Operation

Environment

  • BACnet IP Network
  • Building Operation EnterpriseServer
  • Building Operation Automation Server (AS, AS-P, AS-B)

Cause

According to BACnet routing rules, each BACnet Device should have a unique BACnet Instance ID and each BACnet Network should have a unique BACnet Network ID 

When a BACnet interface is created on an EBO Server, a BACnet IP network is created with default Network ID of 1. This is a local Network address and in not published on the network, it is therefore not a problem if this is duplicated with other EBO Servers. On many site this will remain at 1 for multiple EBO servers with no problems.

If a third party BACnet device uses a published Network ID that is identical to the EBO local Network ID, then it will be ignored.

There will be a "Duplicate of local network"  System Alarm and line similar to below in the trace log

"nsp.pin.BACnet Device <device name>claims to be router to Network #1234 but that is a local network (BACnetMain)"

Resolution

If the EBO Server is not finding a BACnet device on a different network type (via BACnet routing like MSTP or virtual IP) then it could be the Network ID is identical to the local EBO Server Network ID. If this is the case, then simply change the EBO local Network ID and retest.

BACnet Devices on the same IP network, including those on different IP subnets and linked via BBMD or Foreign Devices are not BACnet routed and therefore will not have this issue (no BACnet Network ID route is involved)

Some earlier versions of EBO did not ignore these duplicate Network IDs, thus when up grading some devices could go offline. The workaround would be the same.

The correction to the BACnet operation occurred in v1.9.3 and v2.0.2

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidShore20
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore