Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Configuring branch circuit monitoring

Branch circuit monitoring

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA: Capacity
  • Branch circuit monitoring
  • Configuring branch circuit monitoring
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Branch circuit monitoring
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1012 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring branch circuit monitoring

Picard EcoStruxureIT
‎2019-10-02 02:31 AM

In a Branch Circuit Monitoring configuration, the system works as if you had configured power measurements at rack PDU level, only these measurements are really retrieved at PDU, RDP, or PP level.

You must have a valid ITA: Capacity license to configure Branch Circuit Monitoring.

Modular power distribution

If your data center configuration includes modular power distribution, configure the connection between the power breaker modules and the rack PDUs (Figure 1).

  1. Right-click a modular PDU in the layout, and select Properties.
  2. Click Power and select output voltage.
  3. In Power > Breaker Panel configure the connection between the breaker modules and the rack PDU.
  4. Repeat the above step until all connections have been configured between the breaker modules and the rack PDUs.
  5. Associate the corresponding PDU device to the PDU in the floor layout by dragging it from Unassociated Devices to the PDU in the layout.

Figure 1 Modular Breaker Panel

ITA_modular_breaker_panel_1_360036174554.pngITA_modular_breaker_panel_1_360036174554.png

Non-modular power distribution
If your data center configuration includes non-modular power distribution, you must associate devices and then configure the connection between the expert sensors and the circuit numbers.

  1. Choose Device Association in the Planning pane.
  2. Associate a device to a PDU, RDP, or PP component in the floor layout by dragging it from Unassociated Devices to the component in the layout. 
  3. Sensor Mapping will now appear in the right-click menu of the associated component.
  4. Add sensors by clicking 102240447_360036174554.png102240447_360036174554.png. Use Ctrl-click to add multiple sensors at a time. You can also use the search bar.
  5. The sensors can now be found in the Sensor Mapping table. Click Breaker panel and Position and choose the power values from the drop down menu.
  6. The Multiplier value converts the unit of measurement for the device type into Watts. The Total values must be in Watts. For example, if the measured values are in kW, type 1,000, or if the measured values are in A, type the factor to convert it to Watts.

Notice how the circuit numbers in the breaker panel (Figure 2) match the circuit numbers in Sensor Mapping (Figure 3).

When you have saved your configuration, and the system has retrieved the first measurements from Data Center Expert, Measured Peak Power values appear in Properties > Power Distribution (Figure 1).
It may take a while before they appear, depending on your settings. In System Setup > External System Configuration, you can configure a shorter Power information retrieval interval to see the values quicker.

Figure 2 Non-modular Breaker Panel

ITA_non-modular_breaker_panel_360036174554.pngITA_non-modular_breaker_panel_360036174554.png

Figure 3 Sensor Mapping

ITA_sensor_mapping_360036174554.pngITA_sensor_mapping_360036174554.png

Note

The measured values in Figure 3 are instant values from Data Center Expert whereas the measured values in Figure 1 are peak values gathered over time. Since these values are different in nature, the values differ.

Each time you edit the sensor mappings, the measured data for that device will be deleted (the next time the ITA server gets data from Data Center Expert), and peak and average data will only be collected from that point in time and onwards in contrast to the normal 30 days "catch up" behavior.

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore