Video: UPS Load assessment

Assessments

View recommendations and insights in the UPS Score, UPS Load, Device Security, Alarm, and Active Lifespan Alarms assessments in EcoStruxure IT Expert

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • Reporting
  • Assessments
  • Video: UPS Load assessment
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Assessments
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3592 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Video: UPS Load assessment

Picard EcoStruxureIT
‎2019-09-11 07:20 PM

Last Updated: Sisko JLehr Sisko ‎2025-06-06 09:23 AM

 

 

 

The UPS Load assessment evaluates a period of power load on your UPS. There are three categories: High load, Medium load, and Low load. 

 

 

Screenshot_2019-09-12_at_10_3600352323942740.pngScreenshot_2019-09-12_at_10_3600352323942740.png  

 

How is the UPS load calculated and reflected?

 

The load is evaluated based on the load percentage reported by the device.

 

A High load is at or above 80%.
This indicates possible danger if the load should spike very high.

 

A Medium load is between 25% and 80%.
This indicates a normal expected load for a single phase UPS.

 

A Low load is under 25%.
This indicates you're not currently using the equipment to its fullest potential. You can use this to optimize your data center.

 

ITE UPS load assessment.png

 

Trend analysis

 

ITE UPS load assessment trend.png

 

Load measurements for the device are collected over a minimum of 7 days. A projection is provided for the same period in the future based on the assumption that the load will continue with the same trend. 

 

For example, 30 days after the first measurement is taken from the UPS, the trend displays how that load will look 30 days into the future. This is a total of 60 days from when the first measurement was taken.

 

Continuous measurements are needed for a trend to be reliable. If the device goes offline, or a day of measurement gathering gets skipped, a loss of reliability to create the prediction results. A new projection will not be provided until at least 30 continuous sequential days of load measurements are gathered.

 

What does this mean for you?

 

The load assessment gives you insight into aggregated load information for your UPS devices so you can react intelligently on the possible need to reorganize your equipment.

 

The trend analysis helps you plan ahead to mitigate possible power spikes on the device. In the case of a diminishing trend, you can plan for more optimal power balancing in your data center.

 

Disclaimers

 

  • Make sure the latest version is installed on the Gateway monitoring your UPS.
  • The UPS load assessment is aimed solely at non-redundant setups. Redundancy is not taken into account when a high load warning is reported.
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore