Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
I tried to enable Easergy P5 Protection Relay Virtual Inhections in Esetup Pro, but it doesn't work.
May I know the cause and action?
Best Regards.
Link copied. Please paste this link to share this article on your social media post.
Hello @Hyeontae-Song , hello @CCM ,
Please refer to the history solution as link below.
https://community.se.com/t5/PAE-Protection-Relays-Controllers/P5-Virtual-injections-error/m-p/435732
Link copied. Please paste this link to share this article on your social media post.
Well, just to reply to this because i faced the same problem
- first, i tried from ethernet connection and in manual, it said "local connection is mandatory"
- then i tried to use from virtual machine and look like my company windows policy blocked it (compability problem with winpcap..
finally, i used a clear computer out of the company network and virtual injection worked...
Link copied. Please paste this link to share this article on your social media post.
Hello @Hyeontae-Song , hello @CCM ,
Please refer to the history solution as link below.
https://community.se.com/t5/PAE-Protection-Relays-Controllers/P5-Virtual-injections-error/m-p/435732
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.