Reset HRC to factory default (include IP and password)
Procedure:
- Get a USB stick . (Need to be FAT 32 format)
- Unzip "Reset HRC.zip", Copy files from HRC28IO/HRC42IO folder (depend on the model u want to reset) to the root of USB stick. (Copy the files (PARAM.RAW,UPLOAD.txt),NOT the folder)
- Plug the USB stick into HRC (HRC need to be powered on)
- Unplug the USB stick and reboot HRC
HRC default setting:
IP: 10.0.0.100
Web Account: administrator/password
Labels
- Labels:
-
Hotels
Reply
Replies 2
- Mark as New
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
2017-08-16
11:32 PM
You must have read my mind Peng TANG. I was just thinking about posting a question about this.
I had a HRC which I had forgotten the password. In the end I reloaded the application using SoMachine and it reset, but this method would have saved me a lot of time.